RE: [EnergyPlus_Support] Setpoint Managers are driving me crazy!





No.

I have a reasonable grasp of the basics (at least I think that’s true).  I do not have a good grasp of how SetPointManagers interact and particularly have little – no experience using a pre-cooling coil and making it “play nicely” with the other coils.

 

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Richard Raustad
Sent: Monday, May 21, 2012 12:11 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Setpoint Managers are driving me crazy!

 

Does this help?

Controller:WaterCoil,
  \min-fields 9
  A1 , \field Name
       \type alpha
       \required-field
       \reference AirLoopControllers
  A2 , \field Control Variable
       \type choice
       \key Temperature
       \key HumidityRatio
       \key TemperatureAndHumidityRatio
       \note keys HumidityRatio or TemperatureAndHumidityRatio
       \note requires a ZoneControl:Humidistat object along
       \note with SetpointManager:SingleZone:Humidity:Maximum,
       \note SetpointManager:MultiZone:MaximumHumidity:Average, or
       \note SetpointManager:Multizone:Humidity:Maximum object


On 5/21/2012 11:55 AM, Jim Dirkes wrote:

Dear forum,

Apologies in advance for a messy question…..

Below is a schematic of an air loop. 

·          Note that there is a pre-cooling coil upstream of the Mixing Box.

·         Also note that all of the numbers (e.g., 1200, 1204, etc.) are “shorthand” for a node name.

I want the pre-cooling coil to operate solely as a dehumidification device to maintain a specific humidity ratio.  Everything else should operate in a fairly typical fashion for heating and cooling control, except that there is no economizer.

I show below the SetPointManagers and related mixed air NodeList that I am using with no success for dehumidification.  Can you offer a suggestions to make this work?

Thanks!

 

 

SetpointManager:MixedAir

Name

SPMgr_MixAir_AHU-1

Control variable:

Temperature

reference set point node name

1210  (Node name equivalent)

fan inlet node name

1208

fan outlet node name

1210

Name of the set point Node or Node List

MANodeLIST_AHU-1

 

 

SetPointManager:Warmest

Name

SPMgr_DischAir_AHU-1-warmest

Control Variable

Temperature

HVAC Air Loop Name

AirLoop_AHU-1

Minimum Setpoint Temperature

12.8

Maximum Setpoint Temperature

26.7

Strategy

MaximumTemperature

Setpoint Node or NodeList Name

1210

 

 

SetpointManager:SingleZone:Humidity:Maximum

Name

SPMgr_ZoneRH_AHU-1

Control Variable

MT

Schedule Name

MT

Setpoint Node or NodeList Name

1210

Control Zone Air Node Name

Node_MainStore

 

 

SetPointManager:Scheduled

Name

SPMgr_Sched_AHU-1

Control Variable

Temperature

Schedule Name

SchCpct_Always70F

Setpoint Node or NodeList Name

1204.5  ß E+ complains if I don’t have a temperature setpoint for the pre-cooling coil

 

 

SetPointManager:OutdoorAirPretreat

Name

SPMgr_OAdehum_AHU-1

Control Variable

MaximumHumidityRatio

Minimum Setpoint Temperature

10

Maximum Setpoint Temperature

30

Minimum Setpoint Humidity Ratio

0.0008

Maximum Setpoint Humidity Ratio

0.0091

Reference Setpoint Node Name

1205

Mixed Air Stream Node Name

1205

Outdoor Air Stream Node Name

1204.5

Return Air Stream Node Name

1200

Setpoint Node or NodeList Name

1204.5

 

 

NodeList

Name

MANodeLIST_AHU-1

Node Name1

1205

 

1207

 

1208

 

1204.5

 

 

 

 

 

 

Description: BPT BizCard JVDII Updated

Making me think….

"He who is kind is free, even if he is a slave. He who is evil is a slave, even if he is king." 

 



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
 
UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___