Open studio is not a finished toolset, you may wish to use it only for geometry only.

Below is a workflow that should allow you to create your model. 


First, draw out your geomitry in sketchup/openstudio never saving only as open studio .OSM format and not as sketchup .SKP format, then export as IDF. 

In the IDF editor and name your spaces, save as new filename. 

Import your new IDF into open studio and open the "inspector" feature.

With the inspector check your model space names vs your IDF, if needed update your space names in Open studio. 

Produce final geometry model from Open Studio in .IDF format.

Use IDF editor to create zones from your spaces, copy paste HVAC templates to each zone.

Keep in IDF format for further revision in IDF editor.


Jeremiah D. Crossett
CleanTech Analytics
503-688-8951
www.cleantechanalytics.com


This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics




On Tue, May 22, 2012 at 11:50 AM, juniabuildings <juniabuildings@xxxxxxxxx> wrote:
 


yes. but no answer so far.
thank you anyway.



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> wrote:
>
> Have you tried the OpenStudio forum?
>
> At 12:36 PM 5/22/2012, juniabuildings wrote:
> >hello,
> >
> >I have this problem with OpenStudio. Everytime I close and reopen a
> >file in OpenStudio the name of the Space and Thermal Zone just one text.Like:
> >
> >ThermalZone 1
> >close file and reopen
> >ThermalZone 1ThermalZone 1
> >close file and reopen
> >ThermalZone 1ThermalZone 1ThermalZone 1
> >close file and reopen
> >ThermalZone 1ThermalZone 1ThermalZone 1ThermalZone 1
> >
> >can someone help plese?
> >
> >thank you,
> >
> >Regards
> >
> >
> >
> >
> >
> >------------------------------------
> >
> >Primary EnergyPlus support is found at:
> >http://energyplus.helpserve.com or send a message to
> >energyplus-support@...

> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are currently allowed but be mindful that not everyone
> >has a high speed connection. Limit attachments to small files.
> >
> >EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
> >under the Documentation link and press the "search" button.
> >Yahoo! Groups Links
> >
> >
> >
>




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___