Simge,
You could use SurfaceProperty:OthersideCoefficients to schedule a constant or time varying temperature on the exterior of a surface.
You could then report the below variables and iteratively adjust your otherside coefficients definition until you get the desired temperature / profile
To do this, in the desired BuildingSurface:Detailed, change the outside boundary condition to OtherSideCoefficients and then reference that objects name in the 'Outside Boundary condition object' field. Be sure to read about the otherside coefficients object in the I/O reference as using this will cause the simulation to ignore the external
environment for that surface.
Output:Variable,*,Surface Inside Temperature,hourly; !- Zone Average [C]
Output:Variable,*,Surface Int Adjacent Air Temperature,hourly; !- Zone Average [C]
Hope this helps.
Jason
On Wed, May 23, 2012 at 12:13 PM, Simge Andolsun
<simgeandolsun@xxxxxxxxx> wrote:
Dear EnergyPlus users,
Is it possible to assign a temperature (or a set of varying temperatures) to the inside surface of a construction in EnergyPlus? If there is, could you please describe how it is used?
Thanks in advance,
Best Regards,
Simge Andolsun