Re: [EnergyPlus_Support] double skin facade





If your double wall cavity is truly a corridor and is occupiable space included in ventilation calculations and having its own air terminals, then you will want it to be modeled as its own thermal zone.

If this is not occupiable space,  you may be making the model unnecessarily complex by modeling the cavity as a separate zone.

I would suggest looking into the WindowProperty:AirflowControl & WindowProperty:ShadingControl to see if the options shown there represent your cavity airflow and shading. If yes then you could just model as a wall with a construction with 1.1 m air gap.

If you do end up with the cavity having its own thermal zone, and you want to pass light through this thermal zone to model daylighting sensors on the interior, you will need to model all thermal zones as convex. A formal definition of convex is that any straight line passing through the zone intercepts at most two surfaces. 

Hope this helps.

Jason



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___