[EnergyPlus_Support] Re: Temperature Stratification in a zone
Check out the different RoomAirModel in the ioref.
for example my last simulation...
RoomAirModelType,
Z1 3Node, !- Room-Air Model Name
Z1_Main, !- Zone Name
ThreeNodeDisplacementVentilation, !- Room-Air Modeling Type
Direct; !- Air Temperature Coupling Strategy
RoomAirSettings:ThreeNodeDisplacementVentilation,
Z1_Main, !- Zone Name
SCH_GAIN_DIST, !- Gain Distribution Schedule Name !A value of 1 means that all the convection
!gains from equipment, task lights and people are dispersed in the lower occupied subzone.
!Conversely a value of 0 puts all the lower subzone convective gains into the plumes rising
!into the upper well-mixed subzone
5, !- Number of Plumes per Occupant ...1 CnC operator + 3 servo drives + 1 control cabinet = 5
1, !- Thermostat Height !
1.1, !- Comfort Height !Seated height
.3; !- Temp. Difference Threshold for Displacement Ventilation
!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
RoomAirModelType,
Z2 3Node, !- Room-Air Model Name
Z2_Main, !- Zone Name
ThreeNodeDisplacementVentilation, !- Room-Air Modeling Type
Direct; !- Air Temperature Coupling Strategy
RoomAirSettings:ThreeNodeDisplacementVentilation,
Z2_Main, !- Zone Name
SCH_GAIN_DIST, !- Gain Distribution Schedule Name !A value of 1 means that all the convection
!gains from equipment, task lights and people are dispersed in the lower occupied subzone.
!Conversely a value of 0 puts all the lower subzone convective gains into the plumes rising
!into the upper well-mixed subzone
5, !- Number of Plumes per Occupant ...1 CnC operator + 3 servo drives + 1 control cabinet = 5
1, !- Thermostat Height
1.1, !- Comfort Height
.3; !- Temp. Difference Threshold for Displacement Ventilation
!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
Schedule:Compact,
SCH_GAIN_DIST,
Fraction,
Through: 31 Dec,
For: AllDays,
Until: 06:00, 0.8,
Until: 14:00, 0.8,
Until: 22:00, 0.8,
Until: 24:00, 0.8;
!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
Output:Variable,*,DV Mixed Subzone Temperature,hourly; !- HVAC Average [C]
Output:Variable,*,DV Occupied Subzone Temperature,hourly; !- HVAC Average [C]
Output:Variable,*,DV Floor Subzone Temperature,hourly; !- HVAC Average [C]
Output:Variable,*,DV Transition Height,hourly; !- HVAC Average [m]
Output:Variable,*,DV Fraction Min Recommended Flow Rate,hourly; !- HVAC Average [-]
Output:Variable,*,DV Zone Is Mixed,hourly; !- HVAC Average [1-Yes 0-No]
Output:Variable,*,DV Average Temp Gradient,hourly; !- HVAC Average [K/m]
Output:Variable,*,DV Maximum Temp Gradient,hourly; !- HVAC Average [K/m]
Output:Variable,*,DV Effective Air Temperature for Comfort,hourly; !- HVAC Average [C]
Output:Variable,*,DV Thermostat Temperature,hourly; !- HVAC Average [C]
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/