Thank you Jason, but I think that what you posted is useful if one knows the F-factor value and he wants EnergyPlus to use that value. I  would like to calculate the F-factor of the proposed building (as designed) before I create the model in EnergyPlus, in order to check in the design phase how good the level of insulation is in comparison with the requirements of ASHRAE 90.1.
Best Regards


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jason Kirkpatrick <jason.alan.kirkpatrick@...> wrote:
>
> I suggest you use the object provided for incorporating F-Factor
> 
> Construction:FfactorGroundFloor,
>     ExteriorSlab_PerimeterW, !- Name
>     1.264,                               !- F-Factor {W/m-K}
>     =$ZoneArea,                    !- Area {m2}
>     =$PerimeterDistance;       !- PerimeterExposed {m}
> 
> Be sure to use the F-Factor for the unheated slab on grade floors (required
> in 90.1-2007 App. G3.1.5.b
> "? Slab-on-grade floors shall match the F-factor for unheated slabs from
> the same tables."
> 
> Look in the Engineering Reference for details about how SOG F-Factors are
> calculated, pp 131
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/