Yes, this variable speed approach is a good solution. The plant routines inside EnergyPlus have recently been completely reworked and now it is very likely that branch pumps on demand side are fully supported. (The same general solver is now used for both the demand side and supply side.) This and other expanded flexibility is not yet claimed in the documentation because more detailed testing is needed. As long as you are careful and check the results, it should be okay to push the model in this way. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of ecoeficientees I am using a configuration for branch pumps when in the real HVAC system they are constant flow pumps with bypass (through three-way valves). __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.