[EnergyPlus_Support] Solution to constant branch pumps, when bypass is not possible





I am using a configuration for branch pumps when in the real HVAC system they are constant flow pumps with bypass (through three-way valves).

I use variable speed pumps, setting the curve performance coefficients (1,0,0,0), so power consumption is constant although it can deliver variable flow.

I think it is a good solution to account for a constant pump with bypass, since it provides variable flow but constant power. It is the only way I have found to account for constant pumps as branch pumps, since bypass is not possible.

Do you see it right?

It seems to work ok even with branch pumps in demand side, which should not work according to E+ Reference but Energyplus is not complaining.

That's my second doubt, are branch pumps in demand side correct? As I've said, E+ seems to simulate them right, but Engineering Reference says that pumps in demand side can only be used in the first branch. Why is not Energyplus launching an error, then?

Regards,

Germán Campos.



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___