[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Zone/Sys Sensible Cooling Energy present despite no cooling and no outdoor air





HVAC timestep can at times be shorter than the zone timestep. It would be good to check the output on detailed frequency. 

Output:Variable,*,Zone/Sys Sensible Heating Rate, Detailed;
Output:Variable,*,Zone/Sys Sensible Cooling Rate, Detailed; 

Also you might want to look at the  Predictor-Corrector procedure of energyplus. It is documented in Engineering reference. This small energy consumption could be because of this prediction procedure. It predicts the possible future load and make some heating/cooling so that setpoint is achieved at the desired time. 

You should see this behaviour by adding these variables:
Output:Variable,*,Zone/Sys Sensible Load to Cooling Setpoint Predicted,Detailed; !- HVAC Average [W]
Output:Variable,*,Zone/Sys Sensible Load to Heating Setpoint Predicted,Detailed; !- HVAC Average [W]

Vaibhav Jain
www.vaibhavjain.co




On 27 June 2012 18:25, David Frostclapp <drf10@xxxxxxxxxxx> wrote:
 

When looking at the timestep output from my program I noticed the report variable Zone/Sys Sensible Cooling energy reporting non-zero values despite the temperature of the zone being well below the cooling setpoint at all timesteps.    I began testing the HVAC template example files and noticed the same occurrence despite eliminating the cooling system and outdoor air.   

 

I was hoping someone could explain why the output variable Zone/Sys Sensible Cooling Energy reports cooling values (albeit quite small); however, cooling is completely turned off and there is no outdoor air going to the zone, in addition, I shrunk infiltration to a tiny value. 

 

All wisdom appreciated!

 

David

    




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___