Re: [EnergyPlus_Support] Re: Cooling Load in EnergyPlus





Sorry, I have a question here.

 if Zone/Sys Sensible Cooling Rate does not include any outdoor air brought into the building and then conditioned by coils or heat recovery equipment, then it can be converted to the electricity consumption for cooling?

On Fri, Jun 29, 2012 at 1:30 PM, Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
 

What does the load from the previous model represent (i.e., what are the components of that load)? Did that air loop supply outdoor air to the building? Was the outdoor air load included in the load from the previous model?

The Zone/Sys Sensible Cooling Rate is the delivered capacity to the zone. This does not include any outdoor air brought into the building and then conditioned by coils or heat recovery equipment.

Do you want to know the total coil cooling/heating load? Look to the coils for that information.



On 6/29/2012 1:14 PM, Oluwaseyi Ogunsola wrote:
Hello,

I earlier asked a question about Cooling Load in E+ but I am yet to get any response. 

I am trying to match cooling load from a developed model with that estimated by E+ but I am not sure which of the variables in E+ represent the cooling load. I am thinking the closer variable is the Zone/Sys Sensible Cooling Rate, because the room being modelled has no latent load. I have to be certain about this before proceeding. Please your contribution will be highly appreciated. 

Thanks


From: Oluwaseyi Ogunsola <oluwaseyi.ogunsola@xxxxxxxxx>
To: "EnergyPlus_Support@xxxxxxxxxxxxxxx" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, June 25, 2012 3:41 PM
Subject: Cooling Load in EnergyPlus

Dear All,

I am a new user of EnergyPlus. Please can somebody tell me which of the output variables in EnergyPlus represent cooling load. Awaiting your reply. Thanks,

Oluwaseyi



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years





__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___