[EnergyPlus_Support] Re: ** Warning ** Calculated design cooling load for zone=EXISTINGWORKSHOP:ZONE1



Schedule:Compact,
    ExistingWorkshop:Zone1 Cooling SP Sch,  !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 31 Dec,         !- Field 1
    For: Weekdays SummerDesignDay,  !- Field 2
    Until: 24:00,            !- Field 3
    100,                     !- Field 4
    For: Weekends,           !- Field 5
    Until: 24:00,            !- Field 6
    100,                     !- Field 7
    For: Holidays,           !- Field 8
    Until: 24:00,            !- Field 9
    100,                     !- Field 10
    For: WinterDesignDay AllOtherDays,  !- Field 11
    Until: 24:00,            !- Field 12
    100;                     !- Field 13

No cooling setpoint for the existing workshop?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, CleanTech Analytics <jeremiah@...> wrote:
>
> Thanks Jean- I will look into those suggestions.  Design Builder does this
> sometimes I have noticed...
>  The funny thing about this is that I am modeling a renovation- and this
> part of the building is the non-renovation part so is of less importance
> then the other parts (which are working fine)  So I guess I am hoping for
> an easy fix because this part of the building is not as important to the
> project...
> 
> Thanks again
> 
> 
> 
> 
> *Jeremiah D. Crossett*
> *CleanTech Analytics*
> *503-688-8951*
> *www.cleantechanalytics.com* <http://www.cleantechanalytics.com>
> 
> 
> *
> 
> This document may contain valuable information proprietary to CleanTech
> Analytics which is private and confidential. It may not be shared, copied,
> stored or transmitted in any form without the prior written consent of
> CleanTech Analytics
> *
> 
> 
> 
> On Tue, Jul 3, 2012 at 11:46 PM, Jean marais <jeannieboef@...> wrote:
> 
> > **
> >
> >
> > We've all had this at some point. Unfortunately, there are many possible
> > causes. Report your predicted cooling load (predictor...somthing can't
> > remember the variable name). If there is really no negative values
> > predicted then your zone setpoint or setpoint schedule or designday
> > setpoint schedule may be the problem.
> >
> > If there is a load (negative number for cooling) and the coils are not
> > jumping on, check their schedules, availibility managers, fan control modes
> > and anything else that may stop the fan or coil from jumping on.
> >
> > I may not find time to check your idf in the next 12 hours.
> >
> >  
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/