Re: [EnergyPlus_Support] Set simulation's year





What does your runperiod look like or the "dataperiod" line in the weather file?  That is where the day of week is set though for the custom range object, it may try to look at actual first day of year/day of week.

At 05:53 AM 7/4/2012, garnier.antoine@xxxxxxxxx wrote:
Hi all,

I am currently working on a simulation with a weather file from 2011/01/01 to 2011/12/31.

I set a schedule:compact like that:

         testDimanche
         Temperature
        Through: 12/31
        For: Sunday
        Until: 24:00
        15
        For: AllOtherDays
        Until: 24:00
        20

WhenI run the simulation, the 'testDimanche' variable is shifted by one day. For example, testDimanche equals 15 for the 2011/01/09 (a sunday), but equals 20 for the 2011/01/08 (saturday in 2011, however 2012/01/08 is a sunday).

It looks like EP doesn't consider the weather file year, and use the current year instead.

How can I fix it?

Thanks,




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___