Dear Edwin,

Please find attached svg file for the same. This project has VAV and FCU in different zones. I have used Standard HVAc template to model the same. As my design case doesn't have any heating so i used "Always OFF" schedule for FCU heating so that boiler will not sense any load. I have checked report for boiler Energy consumption and it shows zero. My only concern is there might be some problem at the loop.

Thanks for help!

On Wed, Jul 4, 2012 at 11:31 AM, Edwin Lee <leeed2001@xxxxxxxxx> wrote:
 

It could be, but it would likely be a non-intuitive node connection error.  If it is a blatently invalid topology, that should be trapped early.  However, if components are hooked up in a non-standard way, it may have not been detected, yet the results will be invalid.  I think you will really want to provide a schematic of what you wanted to model, and then provide the svg output of the actual run.


Edwin


On Wed, Jul 4, 2012 at 1:28 PM, Jean marais <jeannieboef@xxxxxxxxx> wrote:
 


one of the earlier warnings mentioned Hot Water Loop. Could there be a node connection mistake?



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Javed Iqbal <eee.javed@...> wrote:
>
> Hi,
>
> I am using Constant Primary and Variable secondary chilled water
> pump. Condenser water pump is also *variable* but hot water pump is *
> constant speed*. All fields are autosize..
>
> thanks
>
> On Wed, Jul 4, 2012 at 10:52 AM, Mário <mneves32@...> wrote:
>
> > **

> >
> >
> > Hello,
> >
> > What kind of pumps, are you using?
> > What is your pump head set to?
> > How are you controling the pump operation?
> >
> > Sometimes when I get these kind of errors in the cooling plant it´s
> > because of the pumps.
> >
> > Best
> >
> > MN
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Edwin Lee <leeed2001@>
> > wrote:
> > >
> > > Are you getting any other errors or warnings? Looks like the loop is out
> > > of control. Some more information on your loop is really needed to
> > > identify the problem.
> > >
> > > Edwin
> > >
> > > On Wed, Jul 4, 2012 at 10:37 AM, Javed Iqbal <eee.javed@> wrote:
> > >
> > > > **
> >
> > > >
> > > >
> > > > Hi All,
> > > >
> > > > I am getting following warning.What could be the possible reason? I am
> > > > trying to model central plant with VAV.
> > > >
> > > > Thanks!
> > > >
> > > > ** Warning ** GetDensityGlycol: Temperature out of range (too high) for
> > > > fluid density
> > > > ************* ** ~~~ ** This error occurred 106213 total times;
> > > > ************* ** ~~~ ** during Warmup 0 times;
> > > > ************* ** ~~~ ** during Sizing 0 times.
> > > > ************* ** ~~~ ** Max=173.136908 {C} Min=100.001832 {C}
> > > > *************
> > > > ************* ** Warning ** Plant loop exceeding upper temperature
> > > > limit, PlantLoop="HOT WATER LOOP HOT WATER LOOP"
> > > > ************* ** ~~~ ** This error occurred 95517 total times;
> > > > ************* ** ~~~ ** during Warmup 0 times;
> > > > ************* ** ~~~ ** during Sizing 0 times.
> > > > ************* ** ~~~ ** Max=173.15264
> > > > *************
> > > > ************* ** Warning ** GetSpecificHeatGlycol: Temperature out of
> > > > range (too high) for fluid specific heat
> > > > ************* ** ~~~ ** This error occurred 3928457 total times;
> > > > ************* ** ~~~ ** during Warmup 0 times;
> > > > ************* ** ~~~ ** during Sizing 0 times.
> > > > ************* ** ~~~ ** Max=173.195998 {C} Min=125.004998 {C}
> > > > *************
> > > > ************* ** Warning ** CoolingTower:VariableSpeed "MAIN TOWER" -
> > > > Tower approach temperature is out of range error continues...
> > > > ************* ** ~~~ ** This error occurred 21 total times;
> > > > ************* ** ~~~ ** during Warmup 0 times;
> > > > ************* ** ~~~ ** during Sizing 0 times.
> > > > ************* ** ~~~ ** Max=1.093516 Min=0.36124
> > > > --
> > > >
> > > >
> > > > Javed Iqbal, LEED AP, CEA
> > > > Energy Analyst
> > > >
> > > >
> > > >
> > > >
> > > >
> > > > --
> > > >
> > > >
> > > > Javed Iqbal, LEED AP, CEA
> > > > Energy Analyst
> > > >
> > > >
> > > >
> > > >
> > >
> > >
> > >
> > > --
> > > Edwin Lee
> > > Doctoral Candidate, Oklahoma State University
> > > ASHRAE Student Member, *Former* ASHRAE OSU Student Branch President
> > > Office: ATRC 303: 405-744-3727
> > >
> >
> >
> >
>
>
>
> --
>
>
> Javed Iqbal, LEED AP, CEA
> Energy Analyst
>




--
Edwin Lee
Doctoral Candidate, Oklahoma State University
ASHRAE Student Member, Former ASHRAE OSU Student Branch President
Office: ATRC 303: 405-744-3727




--


Javed Iqbal, LEED AP, CEA
Energy Analyst   




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
d:\eudora\attach\Proposed Ideal V5_exp.pdf