Thanks drew-
I have been meaning to ask you to shoot me an email when AECOSIM is
updated to e+7.1..

Thanks again

Sent from my Windows Phone
From: Dru Crawley
Sent: 7/4/2012 5:13 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Re: ** Warning ** Calculated design
cooling load for zone=EXISTINGWORKSHOP:ZONE1
Since the schedule is the same for the entire year, a simpler version would
be:

Schedule:Compact,
    ExistingWorkshop:Zone1 Cooling SP Sch,  !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 31 Dec,         !- Field 1
    For: Weekdays SummerDesignDay, Weekends, Holidays, WinterDesignDay,
AllOtherDays,  !- Field 2
    Until: 24:00,            !- Field 3
    100;                     !- Field 4

or even simpler:

Schedule:Compact,
    ExistingWorkshop:Zone1 Cooling SP Sch,  !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 31 Dec,         !- Field 1
    For: AllDays,  !- Field 2
    Until: 24:00,            !- Field 3
    100;                     !- Field 4

On Wed, Jul 4, 2012 at 6:24 PM, CleanTech Analytics <
jeremiah@xxxxxxxxxxxxxxxxxxxxxx> wrote:

> **
>
>
> Thank you so much Jean-
> This is not what it says in Design Builder- I can fix this easy in IDF
> editor but not in the DB interface.
> I guess I will have to submit this to their help desk.
>
> Again thanks- you are a great asset to this list-
>
> Happy 4th and enjoy the Fireworks-!
>
>
> *Jeremiah D. Crossett*
> *CleanTech Analytics*
> *503-688-8951*
> *www.cleantechanalytics.com* <http://www.cleantechanalytics.com>
>
>
> *
>
> This document may contain valuable information proprietary to CleanTech
> Analytics which is private and confidential. It may not be shared, copied,
> stored or transmitted in any form without the prior written consent of
> CleanTech Analytics
> *
>
>
>
> On Wed, Jul 4, 2012 at 12:11 AM, Jean marais <jeannieboef@xxxxxxxxx>wrote:
>
>> **
>>
>>
>> Schedule:Compact,
>> ExistingWorkshop:Zone1 Cooling SP Sch, !- Name
>> Temperature, !- Schedule Type Limits Name
>> Through: 31 Dec, !- Field 1
>> For: Weekdays SummerDesignDay, !- Field 2
>> Until: 24:00, !- Field 3
>> 100, !- Field 4
>> For: Weekends, !- Field 5
>> Until: 24:00, !- Field 6
>> 100, !- Field 7
>> For: Holidays, !- Field 8
>> Until: 24:00, !- Field 9
>> 100, !- Field 10
>> For: WinterDesignDay AllOtherDays, !- Field 11
>> Until: 24:00, !- Field 12
>> 100; !- Field 13
>>
>> No cooling setpoint for the existing workshop?
>>
>>
>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, CleanTech Analytics <jeremiah@...>
>> wrote:
>> >
>> > Thanks Jean- I will look into those suggestions. Design Builder does
>> this
>> > sometimes I have noticed...
>> > The funny thing about this is that I am modeling a renovation- and this
>> > part of the building is the non-renovation part so is of less importance
>> > then the other parts (which are working fine) So I guess I am hoping for
>> > an easy fix because this part of the building is not as important to the
>> > project...
>> >
>> > Thanks again
>> >
>> >
>> >
>> >
>> > *Jeremiah D. Crossett*
>> > *CleanTech Analytics*
>> > *503-688-8951*
>> > *www.cleantechanalytics.com* <http://www.cleantechanalytics.com>
>>
>> >
>> >
>> > *
>> >
>> > This document may contain valuable information proprietary to CleanTech
>> > Analytics which is private and confidential. It may not be shared,
>> copied,
>> > stored or transmitted in any form without the prior written consent of
>> > CleanTech Analytics
>> > *
>> >
>> >
>> >
>> > On Tue, Jul 3, 2012 at 11:46 PM, Jean marais <jeannieboef@...> wrote:
>> >
>> > > **
>>
>> > >
>> > >
>> > > We've all had this at some point. Unfortunately, there are many
>> possible
>> > > causes. Report your predicted cooling load (predictor...somthing can't
>> > > remember the variable name). If there is really no negative values
>> > > predicted then your zone setpoint or setpoint schedule or designday
>> > > setpoint schedule may be the problem.
>> > >
>> > > If there is a load (negative number for cooling) and the coils are not
>> > > jumping on, check their schedules, availibility managers, fan control
>> modes
>> > > and anything else that may stop the fan or coil from jumping on.
>> > >
>> > > I may not find time to check your idf in the next 12 hours.
>> > >
>> > >
>> > >
>> >
>>
>>
>
>

--0016e6db7dd54d341504c40a05d4
Content-Type: text/html; charset="utf-8"
Content-Transfer-Encoding: quoted-printable

<html><head><meta content=3D"text/html; charset=3Dutf-8" http-equiv=3D"Cont=
ent-Type"></head><body><div><div style=3D"font-family: Calibri,sans-serif; =
font-size: 11pt;">Thanks drew- <br>I have been meaning to ask you to shoot =
me an email when AECOSIM is updated to e+7.1.. <br><br>Thanks again<br><br>=
Sent from my Windows Phone<br></div></div><hr><span style=3D"font-family: T=
ahoma,sans-serif; font-size: 10pt; font-weight: bold;">From: </span><span s=
tyle=3D"font-family: Tahoma,sans-serif; font-size: 10pt;">Dru Crawley</span=
><br><span style=3D"font-family: Tahoma,sans-serif; font-size: 10pt; font-w=
eight: bold;">Sent: </span><span style=3D"font-family: Tahoma,sans-serif; f=
ont-size: 10pt;">7/4/2012 5:13 PM</span><br><span style=3D"font-family: Tah=
oma,sans-serif; font-size: 10pt; font-weight: bold;">To: </span><span style=
=3D"font-family: Tahoma,sans-serif; font-size: 10pt;">EnergyPlus_Support@ya=
hoogroups.com</span><br><span style=3D"font-family: Tahoma,sans-serif; font=
-size: 10pt; font-weight: bold;">Subject: </span><span style=3D"font-family=
: Tahoma,sans-serif; font-size: 10pt;">Re: [EnergyPlus_Support] Re: ** Warn=
ing ** Calculated design cooling load for zone=3DEXISTINGWORKSHOP:ZONE1</sp=
an><br><br></body></html>


<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.01//EN" "http://www.w3.org/TR/htm=
l4/strict.dtd">
<html>
<head>
</head>







<body style=3D"background-color: #fff;">
<span style=3D"display:none">&nbsp;</span>

<!--~-|**|PrettyHtmlStartT|**|-~-->
<div id=3D"ygrp-mlmsg" style=3D"position:relative;">
  <div id=3D"ygrp-msg" style=3D"z-index: 1;">
<!--~-|**|PrettyHtmlEndT|**|-~-->

    <div id=3D"ygrp-text" >
     =20
     =20
      <p><div>Since the schedule is the same for the entire year, a simpler=
 version would be:</div><div>=C2=A0</div><div>Schedule:Compact,<br>=C2=A0=
=C2=A0=C2=A0 ExistingWorkshop:Zone1 Cooling SP Sch,=C2=A0 !- Name<br>=C2=A0=
=C2=A0=C2=A0 Temperature,=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=
=C2=A0=C2=A0=C2=A0=C2=A0 !- Schedule Type Limits Name<br>
=C2=A0=C2=A0=C2=A0 Through: 31 Dec,=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=
=A0=C2=A0 !- Field 1<br>=C2=A0=C2=A0=C2=A0 For: Weekdays SummerDesignDay,=
=C2=A0Weekends,=C2=A0Holidays,=C2=A0WinterDesignDay, AllOtherDays,=C2=A0 !-=
 Field=C2=A02<br>=C2=A0=C2=A0=C2=A0 Until: 24:00,=C2=A0=C2=A0=C2=A0=C2=A0=
=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0 !- Field=C2=A03<br>=C2=A0=C2=A0=
=C2=A0 100;=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=
=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0 !- Field 4</div>
<div>=C2=A0</div><div>or even simpler:</div><div>=C2=A0</div><div>Schedule:=
Compact,<br>=C2=A0=C2=A0=C2=A0 ExistingWorkshop:Zone1 Cooling SP Sch,=C2=A0=
 !- Name<br>=C2=A0=C2=A0=C2=A0 Temperature,=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=
=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0 !- Schedule Type Limits Name<br>=
=C2=A0=C2=A0=C2=A0 Through: 31 Dec,=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=
=A0=C2=A0 !- Field 1<br>
=C2=A0=C2=A0=C2=A0 For: AllDays,=C2=A0 !- Field 2<br>=C2=A0=C2=A0=C2=A0 Unt=
il: 24:00,=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=
=A0 !- Field 3<br>=C2=A0=C2=A0=C2=A0 100;=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=
=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=C2=A0=
=C2=A0=C2=A0 !- Field 4<br><br></div><div class=3D"gmail_quote">On Wed, Jul=
 4, 2012 at 6:24 PM, CleanTech Analytics <span dir=3D"ltr">&lt;<a href=3D"m=
ailto:jeremiah@xxxxxxxxxxxxxxxxxxxxxx" target=3D"_blank">jeremiah@cleantech=
analytics.com</a>&gt;</span> wrote:<br>
<blockquote style=3D"border-left-color:rgb(204,204,204);border-left-width:1=
px;border-left-style:solid;" class=3D"gmail_quote">


<u></u>










<div>
<span>=C2=A0</span>


<div>
  <div>


    <div>
     =20
     =20
      <p><font color=3D"#336666"><font face=3D"verdana,sans-serif">Thank yo=
u so much Jean-=C2=A0</font></font><div><font color=3D"#336666" face=3D"ver=
dana, sans-serif">This is not what it says in Design Builder- I can fix thi=
s easy in IDF editor but not in the DB interface.=C2=A0</font></div>


<div><font color=3D"#336666" face=3D"verdana, sans-serif">I guess I will ha=
ve to submit this to their help desk.=C2=A0</font></div><div><font color=3D=
"#336666" face=3D"verdana, sans-serif"><br></font></div><div><font color=3D=
"#336666" face=3D"verdana, sans-serif">Again thanks- you are a great asset =
to this list-=C2=A0</font></div>


<div><font color=3D"#336666" face=3D"verdana, sans-serif"><br></font></div>=
<div><font color=3D"#336666" face=3D"verdana, sans-serif">Happy 4th and enj=
oy the Fireworks-!<br></font><div><font color=3D"#336666"><font face=3D"ver=
dana,sans-serif"><br>


</font></font></div><div><font color=3D"#336666"><font face=3D"verdana,sans=
-serif"><br clear=3D"all"></font></font><div style=3D"text-align:left;"><fo=
nt color=3D"#999999" face=3D"verdana, sans-serif"><i>Jeremiah D. Crossett</=
i></font></div>


<div style=3D"text-align:left;"><font color=3D"#999999" face=3D"verdana, sa=
ns-serif"><i>CleanTech Analytics</i></font></div><div style=3D"text-align:l=
eft;"><font color=3D"#999999" face=3D"verdana, sans-serif"><i><a href=3D"te=
l:503-688-8951" target=3D"_blank" value=3D"+15036888951">503-688-8951</a></=
i></font></div>


<div><div style=3D"text-align:left;"><a href=3D"http://www.cleantechanalyti=
cs.com" target=3D"_blank"><font color=3D"#999999" face=3D"verdana, sans-ser=
if"><i>www.cleantechanalytics.com</i></font></a></div><div><div style=3D"te=
xt-align:center;">


<br></div><div style=3D"text-align:center;"><img src=3D"http://cleantechana=
lytics.com/images/stories/cleantech%20analytics%20120.PNG"><br></div></div>=
</div><div><div><b><p style=3D"text-align:center;" dir=3D"ltr">

<span style=3D"color:rgb(204,204,204);font-family:&quot;Droid Serif&quot;;f=
ont-size:11px;font-style:italic;font-weight:normal;text-decoration:none;ver=
tical-align:baseline;white-space:pre-wrap;">This document may contain valua=
ble information proprietary to CleanTech Analytics which is private and con=
fidential. It may not be shared, copied, stored or transmitted in any form =
without the prior written consent of CleanTech Analytics</span></p>


</b></div></div><br>
<br><br><div class=3D"gmail_quote">On Wed, Jul 4, 2012 at 12:11 AM, Jean ma=
rais <span dir=3D"ltr">&lt;<a href=3D"mailto:jeannieboef@xxxxxxxxx"; target=
=3D"_blank">jeannieboef@xxxxxxxxx</a>&gt;</span> wrote:<br><blockquote styl=
e=3D"border-left-color:rgb(204,204,204);border-left-width:1px;border-left-s=
tyle:solid;" class=3D"gmail_quote">





<u></u>










<div>
<span>=C2=A0</span>


<div>
  <div>


    <div>
     =20
     =20
      <p>Schedule:Compact,<br>
    ExistingWorkshop:Zone1 Cooling SP Sch,  !- Name<br>
    Temperature,             !- Schedule Type Limits Name<br>
    Through: 31 Dec,         !- Field 1<br>
    For: Weekdays SummerDesignDay,  !- Field 2<br>
    Until: 24:00,            !- Field 3<br>
    100,                     !- Field 4<br>
    For: Weekends,           !- Field 5<br>
    Until: 24:00,            !- Field 6<br>
    100,                     !- Field 7<br>
    For: Holidays,           !- Field 8<br>
    Until: 24:00,            !- Field 9<br>
    100,                     !- Field 10<br>
    For: WinterDesignDay AllOtherDays,  !- Field 11<br>
    Until: 24:00,            !- Field 12<br>
    100;                     !- Field 13<br>
<br>
No cooling setpoint for the existing workshop?</p><div><br>
<br>
--- In <a href=3D"mailto:EnergyPlus_Support%40yahoogroups.com"; target=3D"_b=
lank">EnergyPlus_Support@xxxxxxxxxxxxxxx</a>, CleanTech Analytics &lt;jerem=
iah@...&gt; wrote:<br>
&gt;<br>
&gt; Thanks Jean- I will look into those suggestions.  Design Builder does =
this<br>
&gt; sometimes I have noticed...<br>
&gt;  The funny thing about this is that I am modeling a renovation- and th=
is<br>
&gt; part of the building is the non-renovation part so is of less importan=
ce<br>
&gt; then the other parts (which are working fine)  So I guess I am hoping =
for<br>
&gt; an easy fix because this part of the building is not as important to t=
he<br>
&gt; project...<br>
&gt; <br>
&gt; Thanks again<br>
&gt; <br>
&gt; <br>
&gt; <br>
&gt; <br></div>
&gt; *Jeremiah D. Crossett*<br>
&gt; *CleanTech Analytics*<br>
&gt; *<a href=3D"tel:503-688-8951" target=3D"_blank" value=3D"+15036888951"=
>503-688-8951</a>*<br>
&gt; *<a href=3D"http://www.cleantechanalytics.com"; target=3D"_blank">www.c=
leantechanalytics.com</a>* &lt;<a href=3D"http://www.cleantechanalytics.com=
" target=3D"_blank">http://www.cleantechanalytics.com</a>&gt;<div><br>


&gt; <br>
&gt; <br>
&gt; *<br>
&gt; <br>
&gt; This document may contain valuable information proprietary to CleanTec=
h<br>
&gt; Analytics which is private and confidential. It may not be shared, cop=
ied,<br>
&gt; stored or transmitted in any form without the prior written consent of=
<br>
&gt; CleanTech Analytics<br>
&gt; *<br>
&gt; <br>
&gt; <br>
&gt; <br></div>
&gt; On Tue, Jul 3, 2012 at 11:46 PM, Jean marais &lt;jeannieboef@...&gt; w=
rote:<br>
&gt; <br>
&gt; &gt; **<div><br>
&gt; &gt;<br>
&gt; &gt;<br>
&gt; &gt; We&#39;ve all had this at some point. Unfortunately, there are ma=
ny possible<br>
&gt; &gt; causes. Report your predicted cooling load (predictor...somthing =
can&#39;t<br>
&gt; &gt; remember the variable name). If there is really no negative value=
s<br>
&gt; &gt; predicted then your zone setpoint or setpoint schedule or designd=
ay<br>
&gt; &gt; setpoint schedule may be the problem.<br>
&gt; &gt;<br>
&gt; &gt; If there is a load (negative number for cooling) and the coils ar=
e not<br>
&gt; &gt; jumping on, check their schedules, availibility managers, fan con=
trol modes<br>
&gt; &gt; and anything else that may stop the fan or coil from jumping on.<=
br>
&gt; &gt;<br>
&gt; &gt; I may not find time to check your idf in the next 12 hours.<br>
&gt; &gt;<br>
&gt; &gt;  <br>
&gt; &gt;<br>
&gt;<br>
<br>
</div><p></p>

    </div>
    =20

   =20
    <div style=3D"color:rgb(255,255,255);"></div>


</div>



 =20






</div></div></blockquote></div><br></div></div>
<p></p>

    </p></div>
    =20

   =20
    <div style=3D"color:rgb(255,255,255);"></div>


</div>



 =20






</div></div></blockquote></div><br>
</p>

    </div>
    =20

    <!--~-|**|PrettyHtmlStart|**|-~-->
    <div style=3D"color: #fff; height: 0;"></div>
<!--~-|**|PrettyHtmlEnd|**|-~-->

</body>

<!--~-|**|PrettyHtmlStart|**|-~-->
<head>
  <style type=3D"text/css">
  <!--
  #ygrp-mkp {
  border: 1px solid #d8d8d8;
  font-family: Arial;
  margin: 10px 0;
  padding: 0 10px;
}

#ygrp-mkp hr {
  border: 1px solid #d8d8d8;
}

#ygrp-mkp #hd {
  color: #628c2a;
  font-size: 85%;
  font-weight: 700;
  line-height: 122%;
  margin: 10px 0;
}

#ygrp-mkp #ads {
  margin-bottom: 10px;
}

#ygrp-mkp .ad {
  padding: 0 0;
}

#ygrp-mkp .ad p {
  margin: 0;
}

#ygrp-mkp .ad a {
  color: #0000ff;
  text-decoration: none;
}
  #ygrp-sponsor #ygrp-lc {
  font-family: Arial;
}

#ygrp-sponsor #ygrp-lc #hd {
  margin: 10px 0px;
  font-weight: 700;
  font-size: 78%;
  line-height: 122%;
}

#ygrp-sponsor #ygrp-lc .ad {
  margin-bottom: 10px;
  padding: 0 0;
}

  a {
    color: #1e66ae;
  }

  #actions {
    font-family: Verdana;
    font-size: 11px;
    padding: 10px 0;
  }

  #activity {
    background-color: #e0ecee;
    float: left;
    font-family: Verdana;
    font-size: 10px;
    padding: 10px;
  }

  #activity span {
    font-weight: 700;
  }

  #activity span:first-child {
    text-transform: uppercase;
  }

  #activity span a {
    color: #5085b6;
    text-decoration: none;
  }

  #activity span span {
    color: #ff7900;
  }

  #activity span .underline {
    text-decoration: underline;
  }

  .attach {
    clear: both;
    display: table;
    font-family: Arial;
    font-size: 12px;
    padding: 10px 0;
    width: 400px;
  }

  .attach div a {
    text-decoration: none;
  }

  .attach img {
    border: none;
    padding-right: 5px;
  }

  .attach label {
    display: block;
    margin-bottom: 5px;
  }

  .attach label a {
    text-decoration: none;
  }
 =20
  blockquote {
    margin: 0 0 0 4px;
  }

  .bold {
    font-family: Arial;
    font-size: 13px;
    font-weight: 700;
  }

  .bold a {
    text-decoration: none;
  }

  dd.last p a {
    font-family: Verdana;
    font-weight: 700;
  }

  dd.last p span {
    margin-right: 10px;
    font-family: Verdana;
    font-weight: 700;
  }

  dd.last p span.yshortcuts {
    margin-right: 0;
  }

  div.attach-table div div a {
    text-decoration: none;
  }

  div.attach-table {
    width: 400px;
  }

  div.file-title a, div.file-title a:active, div.file-title a:hover, div.fi=
le-title a:visited {
    text-decoration: none;
  }

  div.photo-title a, div.photo-title a:active, div.photo-title a:hover, div=
.photo-title a:visited {
    text-decoration: none;
  }

  div#ygrp-mlmsg #ygrp-msg p a span.yshortcuts {
    font-family: Verdana;
    font-size: 10px;
    font-weight: normal;
  }

  .green {
    color: #628c2a;
  }

  .MsoNormal {
    margin: 0 0 0 0;
  }

  o {
    font-size: 0;
  }

  #photos div {
    float: left;
    width: 72px;
  }

  #photos div div {
    border: 1px solid #666666;
    height: 62px;
    overflow: hidden;
    width: 62px;
  }

  #photos div label {
    color: #666666;
    font-size: 10px;
    overflow: hidden;
    text-align: center;
    white-space: nowrap;
    width: 64px;
  }

  #reco-category {
    font-size: 77%;
  }

  #reco-desc {
    font-size: 77%;
  }

  .replbq {
    margin: 4px;
  }

  #ygrp-actbar div a:first-child {
   /* border-right: 0px solid #000;*/
    margin-right: 2px;
    padding-right: 5px;
  }

  #ygrp-mlmsg {
    font-size: 13px;
    font-family: Arial, helvetica,clean, sans-serif;
    *font-size: small;
    *font: x-small;
  }

  #ygrp-mlmsg table {
    font-size: inherit;
    font: 100%;
  }

  #ygrp-mlmsg select, input, textarea {
    font: 99% Arial, Helvetica, clean, sans-serif;
  }

  #ygrp-mlmsg pre, code {
    font:115% monospace;
    *font-size:100%;
  }

  #ygrp-mlmsg * {
    line-height: 1.22em;
  }

  #ygrp-mlmsg #logo {
    padding-bottom: 10px;
  }

  #ygrp-mlmsg a {
    color: #1E66AE;
  }

  #ygrp-msg p a {
    font-family: Verdana;
  }

  #ygrp-msg p#attach-count span {
    color: #1E66AE;
    font-weight: 700;
  }

  #ygrp-reco #reco-head {
    color: #ff7900;
    font-weight: 700;
  }

  #ygrp-reco {
    margin-bottom: 20px;
    padding: 0px;
  }

  #ygrp-sponsor #ov li a {
    font-size: 130%;
    text-decoration: none;
  }

  #ygrp-sponsor #ov li {
    font-size: 77%;
    list-style-type: square;
    padding: 6px 0;
  }=20

  #ygrp-sponsor #ov ul {
    margin: 0;
    padding: 0 0 0 8px;
  }

  #ygrp-text {
    font-family: Georgia;
  }

  #ygrp-text p {
    margin: 0 0 1em 0;
  }

  #ygrp-text tt {
    font-size: 120%;
  }

  #ygrp-vital ul li:last-child {
    border-right: none !important;=20
  }=20
  -->
  </style>
</head>

<!--~-|**|PrettyHtmlEnd|**|-~-->
</html>
<!-- end group email -->


--0016e6db7dd54d341504c40a05d4--


------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/