RE: [EnergyPlus_Support] poll item (Ensure Air Mass Conservation in a Zone)
It means that E+ does not include mixing and infiltration in the
calulation of return air node flow rate.
Return air node flow rate = Sum(zone supply air node flow rate) -
Sum(Zone exhaust node flow rate).
For most simulations this is accurate.
On Thu, 19 Jul 2012 15:18:46 -0600 Ery Djunaedy
<ery.mailinglist@xxxxxxxxx> wrote:
> All,
>
> In the latest poll, there is one intriguing item for me:
> Ensure Air Mass Conservation in a Zone (all airflows including HVAC,
> exhaust, zone mixing, infiltration, etc.)
>
> Does this mean that at the current state of development, EnergyPlus does
> not ensure air mass conservation in a zone? I do not know what the poll
> item means, I guess. Can someone elaborate on this? Which part of the
> manuals I should read that indicate there is potentially a violation of
> mass conservation in a zone?
>
> Thanks,
>
> Ery
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to
> energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high
> speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/