Re: [EnergyPlus_Support] poll item (Ensure Air Mass Conservation in a Zone)





This is mentioned in the ZoneMixing documentation:
"In EnergyPlus, the ZoneMixing syntax is intended to allow simplified treatment of air
exchange between zones. Note that this statement only affects the energy balance of the
“receiving” zone and that this statement will not produce any effect on the “source” zone.
Mixing statements can be complementary and include multiple zones, but the balancing of
flows between zones is left to the user’s discretion."


On 7/19/2012 5:31 PM, Griffith, Brent wrote:

Hi Ery,

 

The main issue is that so-called simple airflows are not necessarily balanced with HVAC flows.  It is complicated to explain, but for example a user could input a set of ZoneMixing objects that don’t balance out with the air handler.

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Ery Djunaedy
Sent: Thursday, July 19, 2012 3:19 PM
To: EnergyPlus MAILIST
Subject: [EnergyPlus_Support] poll item (Ensure Air Mass Conservation in a Zone)

 

 

All,

In the latest poll, there is one intriguing item for me:
Ensure Air Mass Conservation in a Zone (all airflows including HVAC,
exhaust, zone mixing, infiltration, etc.)

Does this mean that at the current state of development, EnergyPlus does
not ensure air mass conservation in a zone? I do not know what the poll
item means, I guess. Can someone elaborate on this? Which part of the
manuals I should read that indicate there is potentially a violation of
mass conservation in a zone?

Thanks,

Ery




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___