[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: How to set up a Coil:Heating:Water object in a CAV system to controls?
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: How to set up a Coil:Heating:Water object in a CAV system to controls?
- From: "Ke Xu" <xukevin24@xxxxxxxxx>
- Date: Fri, 27 Jul 2012 19:57:04 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Fri, 27 Jul 2012 13:57:08 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1343419027; bh=2IhQrHOB5kU4IORpWLZmh182vaYxg5EwpF3U56ERbO8=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=VEg/SAwpHAqVF7O65smUJH2vhpnxHG8Tg4jWlpqzLM3rshnfJ4ufTJviPLvLi8sCJI+BuW+nzGblfl7CncRK+Zzh31mlzeyqqP6kpCcMwlYUElcgrphXS/R27qxPb4zQ
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=j0VAP9QSDk69BtPGRerdtcqQuXzDekoyFnGQUe0YImr+nByHY+jApKXuemuQbqBqbaRWmmapZ6+0ytdz67ixUjcKyi5bNrJY2xAgIHSZ6rFvoTKXcLn6cxWMLprH3dMA;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <juumf6+nsju@eGroups.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Still couldn't make it work. But Gas furnace will work, see those DOE-reference buildings. My understanding is that the setpointmanager:singlezone:heating is not designed to work with water heating coils in the air loop? anyone test it before?
Thanks.
-Ke
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ke Xu" <xukevin24@...> wrote:
>
> Dear all,
> I am simulating a constant air volume system with a hot-water heating coil in the air-loop, and I am trying to set up controls for coil to maintain supply air temperature set point calculated to maintain the zone temperature. the objects I am using include "Coil: Heating: Water", "Controller: WaterCoil" and "SetpointManager:SingZone:Heating". Somehow, it doesn't work as I expected, the zone temperature in winter time can't be maintained. Any help and comments are appreciated. Thanks in advance.
>
> --Ke
>
> Part of my model related with heating coil is shown below:
>
> Coil:Heating:Water,
> PSZ_1:1_HEATC, !- Name
> Always_On, !- Availability Schedule Name
> Autosize, !- U-Factor Times Area Value {W/K}
> Autosize, !- Maximum Water Flow Rate {m3/s}
> PSZ_1:1 HeatingCoilWaterInlet, !- Water Inlet Node Name
> PSZ_1:1 HeatingCoilWaterOutlet, !- Water Outlet Node Name
> PSZ_1:1_CoolC-PSZ_1:1_HeatCNode, !- Air Inlet Node Name
> PSZ_1:1_HeatC-PSZ_1:1_FanNode, !- Air Outlet Node Name
> UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
> Autosize, !- Rated Capacity {W}
> 82.2222222222222, !- Rated Inlet Water Temperature {C}
> 12.7777781162733, !- Rated Inlet Air Temperature {C}
> 71.1111111111111, !- Rated Outlet Water Temperature {C}
> 43.3333333333334, !- Rated Outlet Air Temperature {C}
> 0.5; !- Rated Ratio for Air and Water Convection
>
> Controller:WaterCoil,
> OS:Controller:WaterCoil 1, !- Name
> Temperature, !- Control Variable
> Normal, !- Action
> Flow, !- Actuator Variable
> PSZ_1:1 Supply Equipment Outlet Node, !- Sensor Node Name
> PSZ_1:1 HeatingCoilWaterInlet, !- Actuator Node Name
> Autosize, !- Controller Convergence Tolerance {deltaC}
> Autosize, !- Maximum Actuated Flow {m3/s}
> 1e-007; !- Minimum Actuated Flow {m3/s}
>
> SetpointManager:SingleZone:Heating,
> SupAirTemp MngrCore_bottom, !- Name
> Temperature, !- Control Variable
> 10.0, !- Minimum Supply Air Temperature {C}
> 43.3333344812747, !- Maximum Supply Air Temperature {C}
> Core_bottom, !- Control Zone Name
> Core_bottom Air Node, !- Zone Node Name
> Core_bottom Direct Air Inlet Node Name, !- Zone Inlet Node Name
> PSZ_1:1 Supply Equipment Outlet Node; !- Setpoint Node or NodeList Name
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/