Re: [EnergyPlus_Support] Temperature Out of Bounds During Warmup



It could be solar. Turn on reporting during warmup and add report variables.

This technique is used to diagnose all problems with a simulation.

Use:
Output:Diagnostics,ReportDuringWarnup;
Output:VariableDictionary,IDF;

Then run the simulation again. Look in the rdd file for report variables 
that could help identify what is causing this.
Outdoor temp
Output:Variable,*,Outdoor Dry Bulb,hourly; !- Zone Average [C]

Zone temp
Output:Variable,*,Zone Mean Air Temperature,hourly; !- Zone Average [C]
Output:Variable,*,Zone/Sys Air Temperature,hourly; !- HVAC Average [C]
Output:Variable,*,Zone/Sys Air Temperature at Thermostat,hourly; !- HV

The zone load
Output:Variable,*,Zone/Sys Sensible Load Predicted,hourly; !- HVAC 
Average [W]
Output:Variable,*,Zone/Sys Sensible Load to Heating Setpoint 
Predicted,hourly; !- HVAC Average [W]
Output:Variable,*,Zone/Sys Sensible Load to Cooling Setpoint 
Predicted,hourly;

Solar through windows
Output:Variable,*,Beam Solar Transmitted through Interior Window,hourly; 
!- Zone Average [W]

There are many others....

Then run the simulation again and look at the simulation output (*.csv)



On 7/30/2012 6:18 PM, ntraughpee wrote:
> I am having this error during the warmup of a new model I am trying to create:
>
>     ** Severe  ** Temperature (high) out of bounds (245.03] for zone="FIRSTNORTH", for surface="961E1D"
>     **   ~~~   **  During Warmup, Environment=RUNPERIOD, at Simulation time=01/01 03:00 - 03:03
>     **   ~~~   ** Zone="FIRSTNORTH", Diagnostic Details:
>     **   ~~~   ** ...Internal Heat Gain [0.000] W/m2
>     **   ~~~   ** ...Infiltration/Ventilation [0.000] m3/s
>     **   ~~~   ** ...Mixing/Cross Mixing [0.000] m3/s
>     **   ~~~   ** ...Zone is part of HVAC controlled system.
>     **  Fatal  ** CalcHeatBalanceInsideSurf: Program terminates due to preceding conditions.
>     ...Summary of Errors that led to program termination:
>     ..... Reference severe error count=1
>     ..... Last severe error=Temperature (high) out of bounds (245.03] for zone="FIRSTNORTH", for surface="961E1D"
>
> Any idea what is causing this? I have never encountered it before and I am flumoxed.
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/