It could be solar. Turn on reporting during warmup and add report variables.
This technique is used to diagnose all problems with a simulation.
Use:
Output:Diagnostics,ReportDuringWarnup;
Output:VariableDictionary,IDF;
Then run the simulation again. Look in the rdd file for report variables
that could help identify what is causing this.
Outdoor temp
Output:Variable,*,Outdoor Dry Bulb,hourly; !- Zone Average [C]
Zone temp
Output:Variable,*,Zone Mean Air Temperature,hourly; !- Zone Average [C]
Output:Variable,*,Zone/Sys Air Temperature,hourly; !- HVAC Average [C]
Output:Variable,*,Zone/Sys Air Temperature at Thermostat,hourly; !- HV
The zone load
Output:Variable,*,Zone/Sys Sensible Load Predicted,hourly; !- HVAC
Average [W]
Output:Variable,*,Zone/Sys Sensible Load to Heating Setpoint
Predicted,hourly; !- HVAC Average [W]
Output:Variable,*,Zone/Sys Sensible Load to Cooling Setpoint
Predicted,hourly;
Solar through windows
Output:Variable,*,Beam Solar Transmitted through Interior Window,hourly;
!- Zone Average [W]
There are many others....
Then run the simulation again and look at the simulation output (*.csv)> ------------------------------------
On 7/30/2012 6:18 PM, ntraughpee wrote:
> I am having this error during the warmup of a new model I am trying to create:
>
> ** Severe ** Temperature (high) out of bounds (245.03] for zone="FIRSTNORTH", for surface="961E1D"
> ** ~~~ ** During Warmup, Environment=RUNPERIOD, at Simulation time=01/01 03:00 - 03:03
> ** ~~~ ** Zone="FIRSTNORTH", Diagnostic Details:
> ** ~~~ ** ...Internal Heat Gain [0.000] W/m2
> ** ~~~ ** ...Infiltration/Ventilation [0.000] m3/s
> ** ~~~ ** ...Mixing/Cross Mixing [0.000] m3/s
> ** ~~~ ** ...Zone is part of HVAC controlled system.
> ** Fatal ** CalcHeatBalanceInsideSurf: Program terminates due to preceding conditions.
> ...Summary of Errors that led to program termination:
> ..... Reference severe error count=1
> ..... Last severe error=Temperature (high) out of bounds (245.03] for zone="FIRSTNORTH", for surface="961E1D"
>
> Any idea what is causing this? I have never encountered it before and I am flumoxed.
>
>
>> Yahoo! Groups Links
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>
>
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years