[EnergyPlus_Support] Re: queries
1) 70 W/Person is for someone in a coma. This warning is just saying that this looks suspicious, you may want to double check your values. They must be for the total W/person, not just the sensible heat.
2) You have tilted constructions that are defined differently than the standard ASHRAE definition for wall, floor or roof. This is just a warning saying you may want to define a roof as a wall for example. I'm not sure if this has accuracy implications...possibly convection coeff assignation by the algorithm used.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Evi Emmanouil <evi_emmanouil@...> wrote:
>
> Would anyone help me with these?
>
>
> ** Warning ** GetInternalHeatGains: People=DIADROMOI", Activity Level Schedule Name falls outside typical range [70,1000] W/person for Thermal Comfort Reporting.
> ** ~~~ ** Schedule="LEASONSACTIVITYSCHEDULE; Odd comfort values may result. Entered min/max range=[0.0,1.0] W/person.
>
> ** Warning ** WriteVeriSumTable: InputVerificationsAndResultsSummary: Wall area based on [>=60,<=120] degrees (tilt) as walls
> ** ~~~ ** differs ~20.4% from user entered Wall class surfaces. Degree calculation based on ASHRAE 90.1 wall definitions.
> ** ~~~ ** Calculated based on degrees=[11762.055] m2, Calculated from user entered Wall class surfaces=[9770.264] m2.
> ** ~~~ ** Check classes of surfaces and tilts for discrepancies.
> Thanks in advance!
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/