Just because you don't need to be bring OA in at night doesn't mean that you don't need to condition the zones, which means the supply fan must turn on. During the day, the fan runs continuously to ensure the proper amount of OA, during the night, if there is a load, the fan turns on and off with the coils. There is usually a fan operating mode schedule used with HVAC equipment that can cycle, or you can use a night ventilation manager to cycle the fan on for VAV systems. OA control is independent of fan operation (i.e., you can have OA or not if the fan is running). On 8/16/2012 10:12 AM, Carolina
Galeazzi wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.