E+ uses “efficiency “ in a way that is somewhat confusing: “Motor Efficiency” = motor efficiency (e.g. .92) “Fan Efficiency” = Fan mechanical efficiency * motor efficiency (e.g., .50 * .92 = .46) James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of FrancescoP This discussion was very useful, but now I have a new question. ASHRAE 90.1-2007 provides a method to calculate the "Fan motor Efficiency". As I'm modelling a VAV system with reheat, I'm using the object Fan:VariableVolume
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.