Jean, If the heating setpoint is 20 and cooling setpoint is 26, the air delivered to the zone should be: 20 + 11.1 = 31.1 (maximum) for heating needs 26 - 11.1 = 14.9 (minimum) for cooling needs. These values are set in the Sizing:System, Central cooling design supply air temperature = 14.9 And Sizing:Zone, Zone heating design supply air temperature = 31.1 James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:Energ
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.