No, it means that if the reheat coils are operating during the cooling 
season, which they sometimes do, that the zone temp will be controlled 
to the thermostat heating set point (20C). If the zones are over-cooled 
and require that the reheat coils turn on, the air temperature in the 
supply duct after the reheat coils will be whatever it needs to be to 
bring the zone temp back up to to 20C.

Run a simulation and review the zone temp when the reheat coils are 
active. The zone temp should be maintained at the zone thermostat 
heating set point temperature. You can then look at the supply air temp 
leaving the reheat coil and see what temperature that node is.

On 8/29/2012 10:08 AM, Jean marais wrote:
> Richard said: "E+ will control the reheat coils to the heating setpoint when the system is in cooling mode"
>
> This means that if my heating (winter) zone setpoint is 20 deg C, then the air delivered after reheat in cooling mode will be 20 deg C.
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/