1) no economizer, no heat recovery
2) mixture...recirculates 100% - the min ODA that you specify in the objects
3) I don't think node specifications are required. This is not an Airloop as such. Think of it more as a calculation. Your sizing:zone object should contain most of the info required for the calculation. The Ideal Air system fullfills those requirements.
I've not used this object except via DesignBuilder, so I'm no expert here. Find out the nittty gritty by checking examples in your example folder. Then let me know.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ladan" <ladan_joon@...> wrote:
>
> Hello,
>
> My name is Ladan and I have recently started working with E+. I appreciate if you help me figure out how "Ideal Loads Air System" works.
> My question is:
>
> ? Does the Ideal Load system employ economizer and heat recovery system even though they are not specified in the idf file and left blank in the inputs?
>
> ? Is the airflow supplied from outside (outdoor air) in an ideal loads system or is it a mix from outside air and return air from the zone?
>
> ? I'd like to know if I should define an exhaust node for my system, because only an inlet node is required in the idf file.
>
> ? Does the Ideal Loads air system assume a VAV system (variable air volume) with constant supply air temperature for loads calculations? or it totally ignores the type of system?
>
> Thank you very much in advance. Your help is really appreciated.
>
> Ladan Ghobad
>