Fwd: [EnergyPlus_Support] Re: How does Ideal Loads Air System function?





Actually the Ideal Loads can be set to use heat recovery and economizer but only if you specify it; It's definitely my favorite object in E+. 

1. No unless you specify Ideal Air loads won't use heat recover or economizer.
2. There is no pump/fans modeled so this question is somewhat meaningless. It would be best to think of the system as being pure outdoor air supply but since there is no "cost" to recirculate air you can think of any ratio you want producing the same answer.
3. I think the exhaust node is only used for heat recovery so if your not recovering heat it is not needed.
4. The ideal air loads system is implemented as a VAV system but it is PFM (Pure F...ing Magic). It basically just adds/subtracts heat directly from the zone without considering most of the things you would typically model in E+ like the HVAC system. So unless you put in a capacity or air temperature limit into the idealAirLoads object it will essentially vary the input air temperature to meet both airflow required and temperature required. 

The standard format is in the input/output manual so I didn't paste it here.

Jason
---------- Forwarded message ----------
From: Jean marais <jeannieboef@xxxxxxxxx>
Date: Wed, Aug 29, 2012 at 3:13 PM
Subject: [EnergyPlus_Support] Re: How does Ideal Loads Air System function?
To: EnergyPlus_Support@xxxxxxxxxxxxxxx


 

1) no economizer, no heat recovery
2) mixture...recirculates 100% - the min ODA that you specify in the objects
3) I don't think node specifications are required. This is not an Airloop as such. Think of it more as a calculation. Your sizing:zone object should contain most of the info required for the calculation. The Ideal Air system fullfills those requirements.

I've not used this object except via DesignBuilder, so I'm no expert here. Find out the nittty gritty by checking examples in your example folder. Then let me know.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ladan" <ladan_joon@...> wrote:
>
> Hello,
>
> My name is Ladan and I have recently started working with E+. I appreciate if you help me figure out how "Ideal Loads Air System" works.
> My question is:
>
> ? Does the Ideal Load system employ economizer and heat recovery system even though they are not specified in the idf file and left blank in the inputs?
>
> ? Is the airflow supplied from outside (outdoor air) in an ideal loads system or is it a mix from outside air and return air from the zone?
>
> ? I'd like to know if I should define an exhaust node for my system, because only an inlet node is required in the idf file.
>
> ? Does the Ideal Loads air system assume a VAV system (variable air volume) with constant supply air temperature for loads calculations? or it totally ignores the type of system?
>
> Thank you very much in advance. Your help is really appreciated.
>
> Ladan Ghobad
>




--
Jason Quinn
Lead Engineer
Sustainable Engineering Ltd.
82 Liverpool Street
Wanganui 4500
New Zealand

+64 21 1846 911


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___