Try changing the order of the zone equipment. Air terminals are for air
loops, which are simulated first. I believe we corrected this in V7 or
somewhere around that time (meaning it shouldn't matter). If this works,
then please send the previous input file to the help desk.
support@xxxxxxxxxxxxxxxxxxxxxxxx
Use:
ZoneHVAC:EquipmentList :
AirTerminal:SingleDuct:Uncontrolled (SEQUENCE 1)
ZoneHVAC:FourPipeFanCoil (SEQUENCE 2)
On 9/20/2012 7:11 PM, andresdagm wrote:
> Thank you for your help.
>
> i dont know if I am doing something wrong, my fan coil unit dont met
> the setpoint temperature during occupied hours, i im using this
>
> ZoneHVAC:EquipmentList :
>
> ZoneHVAC:FourPipeFanCoil (SEQUENCE 1)
>
> AirTerminal:SingleDuct:Uncontrolled (SEQUENCE 2)
>
>
>
> Any help, thank you
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jim Dirkes <jim@...> wrote:
>> You might consider using a Fan:VariableVolume and also define the fan
> such that the minimum flow is the same as low speed and the power
> coefficients are linear between low speed power and high speed power....
> something like what I show below.
>>
>> [cid:image001.png@...]
>>
>> James V Dirkes II, PE, BEMP, LEED AP
>>
> www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
>> Energy Analysis, Commissioning & Training Services
>> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
>> 616 450 8653
>>
>> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of andresdagm
>> Sent: Tuesday, September 18, 2012 9:22 AM
>> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>> Subject: [EnergyPlus_Support] Fan coil two velocity
>>
>>
>>
>> good morning,
>>
>> i am wondering who may I model a fan coil two velocity (off/low/high)
>> this fan coil only work for cooling
>> Also how can i do to set up the setpoint temperature.
>> I generally work in DB and I hav e export this equpment (including
> chillers,fan for ventilation..) but I am in troubles with this.
>> thank you
>>
>
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/