thank you, it works.
I use DB 3.0.105 and EnergyPlus 7.0, maybe it is the reason why this feature was not corrected.
Dante García
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Try changing the order of the zone equipment. Air terminals are for air
> loops, which are simulated first. I believe we corrected this in V7 or
> somewhere around that time (meaning it shouldn't matter). If this works,
> then please send the previous input file to the help desk.
> support@...
>
> Use:
>
> ZoneHVAC:EquipmentList :
>
> AirTermnal:SingleDuct:Uncontrolled (SEQUENCE 1)
>
> ZoneHVAC:FourPipeFanCoil (SEQUENCE 2)
>
> On 9/20/2012 7:11 PM, andresdagm wrote:
> > Thank you for your help.
> >
> > i dont know if I am doing something wrong, my fan coil unit dont met
> > the setpoint temperature during occupied hours, i im using this
> >
> > ZoneHVAC:EquipmentList :
> >
> > ZoneHVAC:FourPipeFanCoil (SEQUENCE 1)
> >
> > AirTerminal:SingleDuct:Uncontrolled (SEQUENCE 2)
> >
> >
> >
> > Any help, thank you
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jim Dirkes <jim@> wrote:
> >> You might consider using a Fan:VariableVolume and also define the fan
> > such that the minimum flow is the same as low speed and the power
> > coefficients are linear between low speed power and high speed power....
> > something like what I show below.
> >>
> >> [cid:image001.png@]
> >>
> >> James V Dirkes II, PE, BEMP, LEED AP
> >>
> > www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> >> Energy Analysis, Commissioning & Training Services
> >> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> >> 616 450 8653
> >>
> >> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of andresdagm
> >> Sent: Tuesday, September 18, 2012 9:22 AM
> >> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >> Subject: [EnergyPlus_Support] Fan coil two velocity
> >>
> >>
> >>
> >> good morning,
> >>
> >> i am wondering who may I model a fan coil two velocity (off/low/high)
> >> this fan coil only work for cooling
> >> Also how can i do to set up the setpoint temperature.
> >> I generally work in DB and I hav e export this equpment (including
> > chillers,fan for ventilation..) but I am in troubles with this.
> >> thank you
> >>
> >
> >
> >
> >
> > ------------------------------------
> >
> > Primary EnergyPlus support is found at:
> > http://energyplus.helpserve.com or send a message to energyplus-support@...
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/