Fabiano, It sounds as though you are using the correct “tools” in EnergyPlus. Report the zone temperatures during the unoccupied periods and compare to the zone setpoint. If the temperature does not exceed the setpoint in the cooling season or fall below the setpoint in the heating season, then the fan should remain off. p.s., EnergyPlus assumes that a zone is in the “occupied” period whenever any people are present. If your People object schedule shows non-zero values (e.g. 0.02), then it is an “occupied” period. James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of fabiano.ferreiracw
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.