Re: [EnergyPlus_Support] Output Variable to Calculate the Zone Load Requirements



One of the best ways to understand this is to report the zone temp, 
humidity ratio, and enthalpy along with the zone inlet node temp, 
humidity ratio, and enthalpy. Also report the zone inlet node mass flow 
rate.

You can then calculate the zone energy entering the zone through the 
zone inlet node. Q = Mdot(deltaH)

Zone/Sys Sensible Cooling or Heating  Energy only report what enters the 
zone through the zone inlet node. It does not include any effects of 
outdoor air or fan heat.

The ideal loads total heating and ideal loads zone total heating show 
the same value and is an enthalpic calculation (includes impact of 
moisture difference between zone inlet node and zone node), the ideal 
loads sensible variables only show the impact of temperature difference 
between the zone inlet node and zone node.

It depends on what your goal is as to which report variables to use. Do 
you want to know the energy impacts of outdoor air? Or just the energy 
required to meet the standard zone loads?

On 10/4/2012 1:53 AM, kontadakisantonios wrote:
> Hello,
> I usually use a HVACTemplate:Zone:IdealLoadsAirSystem in order to calculte the annual requirements for heating and cooling of a zone.
> In the Output:Variable there are several variables from which you can take the Energy loads:
>
> #A#"Zone/Sys Sensible Cooling Energy" & :Zone/Sys Sensible Heating Energy";
>
> #B1# "Ideal Loads Total Heating Energy" & "Ideal Loads Total Cooling Energy";
> #B2# "Ideal Loads Sensible Cooling Energy" & "Ideal Loads Sensible Heating Energy"
>
> #C1# "Ideal Loads Zone Total Heating Energy" & "Ideal Loads Zone Total Cooling Energy"
> #C2# "Ideal Loads Zone Sensible Heating Energy" & "Ideal Loads Zone Sensible Cooling Energy"
>
> Those three output sets give different Annual/Summary loads (J), for example in an South oriented office room of 18.36 m2 located in Athens-Greece the annual loads for heating and cooling are:
> #A#  Zone/Sys Sensible_Heating=324957402J, Cooling= 3557071988J
> #B1# IdealLoads Total_ Heating=404805597.1J, Cooling=4261318764J
> #B2# IdealLoads Sensible_Heating=326646181.2J, Cooling=3562938318J
> #C1# IdealLoads Zone Total_Heating=404807810.5J, Cooling=4261320977J
> #C2# IdealLoads Zone Sensible_Heating=326645932.9J, Cooling=3562934397J
>
> The main question is:
> "In order to calculate the annual or monthly requirements of a space for heating and cooling when using an ideal Load HVAC System which output set i request?"
> Please if possible explain the difference between the output viarable sets and when we use them.
>
> Any help to better understand E+ would be appreciated
> Thank you in advance very much
> Antonis.
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/