1. Keep in mind that there is a normal requirement for a Baseline system to be modeled as one system per floor. (That probably won?t affect your outcome very much, but it may save trouble from the LEED reviewer.)
2. The Baseline airflow will not be the same as Proposed. Baseline systems must be sized with 11.1C delta temperature and Proposed systems are often sized differently. In addition the loads will differ for Baseline / Proposed due to different wall and glazing. Both of these factors will combine to produce different airflows.
3. Cooling load is met exclusively by the Air Loop discharge temperature (Room temp of ~ 23C ? 11.1C = ~12.2C discharge temp)
James V Dirkes II, PE, BEMP, LEED AP
<http://www.buildingperformanceteam.com/>www.buildingperformanceteam.com
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=27039/stime=1349366380>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmZzM0bWFmBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzNDkzNjYzODA->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkaGh2amdmBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzQ5MzY2Mzgw>Visit Your Group | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___