Hello,
I think what you need is to set the field "Type of Load to Size On" from the Sizing:System object to: VentilationRequirement.
Best Regards
Mn
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "direzionecontraria" <direzionecontraria@...> wrote:
>
> I have created a model in DesignBuilder and now I'm analyzing and modifying it in EnergyPlus.
> I have no natural ventilation. I have AHUs that serve more than one zone. I wonder how mechanical ventilation is distributed among the different zones.
> I'm sizing the HVAC system with a SizingPeriod:DesignDay for winter season and a SizingPeriod:DesignDay for summer season.
> There are the objects DesignSpecification:OutdoorAir but they are referred only by Sizing:Zone objects.
> I think that Sizing:Zone objects are used only during sizing, not during the RunPeriod (e.g. annual simulation), right? So I am wondering how mechanical ventilation is distributed among the different zones for the RunPeriod with weather file. Should I use a particular object to specify the ventilation conditions during the RunPeriod?
> Best Regards
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/