[EnergyPlus_Support] Re: How To Change Warning into Fatal Error? (schedule:file CSV line endings)
One partial solution to the line-endings issue is to select the MSDOS format option in excel, rather than the standard CSV option. (Again, this only applies to those using excel for mac, generating CSVs for use as input schedules)
1. In excel: choose save-as
2. select "MS-DOS Comma Separated (.csv)" as the file format.
The WRONG choice is: "Comma Separated Values (.csv)" as the file format.
Cheers,
Ryan
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ryan_Element" <ryan_element@...> wrote:
>
> Linda, here is the warning text from my .ERR file:
>
> ** Warning ** ProcessScheduleInput: Schedule:File="OFFICE OCCUPANCY" less than specified hourly values read from file.
> ** ~~~ ** ..Specified Number of Hourly Values=8760 Actual number of hourly values included=2
>
>
> I will submit this to the help desk now. Thanks for your help!
>
> Ryan
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@> wrote:
> >
> > You don't say what the warning is. Nor provide any example (examples
> > should be submitted to the helpdesk so we can incorporate this).
> >
> > I can't offhand think of a warning of this nature that would not
> > cause a fatal but obviously you have encountered it.
> >
> > There is not control for a user to be able to change the
> > warning/severe/fatal nature of EnergyPlus messages -- we have not
> > considered it before.
> >
> > At 10:52 AM 10/11/2012, Ryan_Element wrote:
> > >Greetings,
> > >
> > >I would like to change certain energyplus-warnings into fatal errors, so that
> > >instead of running after issuing a certain warning, the simulation will be
> > >terminated.
> > >
> > >I found the Output:PreprocessorMessage object in the I/O reference,
> > >but I'm not
> > >sure how to use it - or even if it's the right approach.
> > >
> > >WHY would I want this, you ask? Because there is one warning (IMO) that should
> > >be an error, and should cause the simulation to terminate...I use the
> > >schedule:file object to reference several schedules stored in a CSV file.
> > >Occasionally I edit this CSV file using excel on my apple computer.
> > >When I save
> > >the CSV file in excel, the line-endings are set as
> > >macintosh-text-file-line-endings. After saving the CSV with mac-based-line
> > >endings, I run my energyplus simulation on my apple computer. Sadly,
> > >energyplus
> > >cannot read text files with mac-based line-endings, so it issues a warning to
> > >that effect, but continues to run - WITHOUT the schedules it was intended to
> > >use.
> > >
> > >I can circumvent this issue by re-saving the CSV file in a text editor and
> > >specifying that it should have unix-based-line-endings. With
> > >unix-based-line-endings, the file is readable by energyplus, and my simulation
> > >works properly. This is truly annoying, as I edit the CSV file regularly, and
> > >don't want to go through the additional steps of re-saving it with unix-based
> > >line-endings each time. It is also annoying because IF I forget to re-save the
> > >CSV file, the simulation still runs without an error, and I don't realize that
> > >anything is amiss until I view the bogus results, ponder why the results are
> > >bogus, remember to check on the CSV file line-endings, and so on.
> > >
> > >Thanks for your help
> > >
> > >Ryan
> > >
> > >
> > >
> > >
> > >------------------------------------
> > >
> > >Primary EnergyPlus support is found at:
> > >http://energyplus.helpserve.com or send a message to
> > >energyplus-support@
> > >
> > >The primary EnergyPlus web site is found at:
> > >http://www.energyplus.gov
> > >
> > >The group web site is:
> > >http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > >Attachments are currently allowed but be mindful that not everyone
> > >has a high speed connection. Limit attachments to small files.
> > >
> > >EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
> > >under the Documentation link and press the "search" button.
> > >Yahoo! Groups Links
> > >
> > >
> > >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/