I think you mean the variable of WindExt used in Qw calculation at
HVACManager.f90(2564):
Qw =
Cw*Ventilation(J)%OpenArea*GetCurrentScheduleValue(Ventilation(J)%OpenAreaSc
hedPtr)*WindExt
The WindExt is determined by the following line at
HVACManager.f90(2394)
WindExt = Zone(NZ)%WindSpeed
The Zone wind speed is determined by zone height at
HeatBalanceSurfaceManager.f90(281):
Zone(ZoneNum)%WindSpeed = WindSpeedAt(Zone(ZoneNum)%Centroid%Z)
Therefore, the wind speed used in the Ventilation by Wind and Stack
with
Open Area object is a local wind speed.
Hope this helps.
Lixing
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of
wanghaojie630
Sent: Wednesday, October 17, 2012 11:26 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Problem with Ventilation by Wind and
Stack
with Open Area
I notice in the Engineering Reference the equation for ventilation
by wind
and stack uses local wind velocity to calculate the ventilation rate
by
wind, however, when I look into the source code for EP 7.1, the
velocity
seems to be the external wind velocity, which means it is the
velocity at 10m height. So I wonder if I miss something or the code
might be
wrong?
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to
energyplus-support@...
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone
has a
high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the
Documentation link and press the "search" button.
Yahoo! Groups Links