Re: [EnergyPlus_Support] VRF water-cooled condensers.





No, i was just testing it.



De: Richard Raustad <RRaustad@xxxxxxxxxxxx>
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
Enviado: Jueves 25 de octubre de 2012 17:47
Asunto: Re: [EnergyPlus_Support] VRF water-cooled condensers.

 
Really, the outdoor air temperature is 60C ?

Seems more like a water temperature to me.

I think it's just the warning message that needs correcting.

On 10/25/2012 6:18 AM, Omar Tabuyo wrote:
Hi,

I understand the warning message meaning. I have increased  Heating Maximum Outdoor Dry-Bulb Temperature, but the  Outdoor Dry-Bulb Temperature  also incease. 

   ** Warning ** AirConditioner:VariableRefrigerantFlow "VRF EXTERIORUNIT01 PBYP1".
   **   ~~~   ** ...InitVRF: VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode Limits have been exceeded and VRF system is disabled.
   **   ~~~   ** ... Outdoor Dry-Bulb Temperature                 = 60.097
   **   ~~~   ** ... Heating Minimum Outdoor Dry-Bulb Temperature = -20.000
   **   ~~~   ** ... Heating Maximum Outdoor Dry-Bulb Temperature = 60.000
   **   ~~~   ** ... Check VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode limits.
   **   ~~~   **  During Warmup, Environment=BARCELONA INVIERNO, at Simulation time=01/01 08:30 - 08:45

I am trying to simulate a VRF water condenser. In proyect, the water temperature is defined between 35ºC and 20ºC, so, I should include a boiler and a cooling tower in the condenser loop.

So, my doubt is  Which is the Heating Min/Max Outdoor Dry-Bulb Temperature infuence in the VFR water condenser?

I am thinking the problem may lie the curves, because i am using the VRF example curves. Any other idea?

Have anyone an example for water condenser exterior unit curves?

thanks


De: YuanLu Li <yli006@xxxxxxxxxxx>
Para: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx>
Enviado: Miércoles 24 de octubre de 2012 21:45
Asunto: RE: [EnergyPlus_Support] VRF water-cooled condensers.

 


I have no idea how your system is operating.
 
** Warning ** AirConditioner:VariableRefrigerantFlow "VRF EXTERIORUNIT01 PBYP1".
** ~~~ ** ...InitVRF: VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode Limits have been exceeded and VRF system is disabled.
** ~~~ ** ... Outdoor Dry-Bulb Temperature = 35.077
** ~~~ ** ... Heating Minimum Outdoor Dry-Bulb Temperature = -20.000
** ~~~ ** ... Heating Maximum Outdoor Dry-Bulb Temperature = 35.000
** ~~~ ** ... Check VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode limits.
** ~~~ ** During Warmup, Environment=BARCELONA INVIERNO, at Simulation time=01/01 19:00 - 19:15
 
The warning message is clera.    35.077 is larger than 35.00.
 
Outdoor dry bulb temperature is your environment temperature.
 
 Dr. Li  

 


To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: omartabuyo@xxxxxxxxx
Date: Wed, 24 Oct 2012 18:56:07 +0100
Subject: Re: [EnergyPlus_Support] VRF water-cooled condensers.

 
i used you advice to build the model, but when running this warning is showed:

   ** Warning ** AirConditioner:VariableRefrigerantFlow "VRF EXTERIORUNIT01 PBYP1".
   **   ~~~   ** ...InitVRF: VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode Limits have been exceeded and VRF system is disabled.
   **   ~~~   ** ... Outdoor Dry-Bulb Temperature                 = 35.077
   **   ~~~   ** ... Heating Minimum Outdoor Dry-Bulb Temperature = -20.000
   **   ~~~   ** ... Heating Maximum Outdoor Dry-Bulb Temperature = 35.000
   **   ~~~   ** ... Check VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode limits.
   **   ~~~   **  During Warmup, Environment=BARCELONA INVIERNO, at Simulation time=01/01 19:00 - 19:15

Anyone kown how i can solve it? Which is the Heating Min/Max Outdoor Dry-Bulb Temperature infuence in the VFR water condenser?

thanks



De: Richard Raustad <RRaustad@xxxxxxxxxxxx>
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
Enviado: Lunes 22 de octubre de 2012 19:01
Asunto: Re: [EnergyPlus_Support] VRF water-cooled condensers.

 
Yes, use a single plant loop to serve the VRF condenser.
Here's a file I have been playing with.
The imf file is the building and VRF system.
The idf is the plant loop.
The in.idf file is these two files after EPMacro assembles them together.

On 10/22/2012 12:47 PM, Omar Tabuyo wrote:
Dear all,

I am trying to simulate a VRF water condenser. I know that you can do it with version 7.2. In proyect, the water temperature is defined between 35ºC and 20ºC, so, I should include a boiler in the condenser loop.

Is this configuration possible today in energyplus? Anyone know how i can simulate it?

Thanks in advance


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years






-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___