If you use one of the weather files that come with EnergyPlus or are
on the E+ web site, there is a .DDY file which is contains the design
days for that locations (if there are design data in the ASHRAE 2009
Fundamentals for that location). If you have a file that you have
created, the WeatherConverter (Weather Statistics and Converter) will
create a .DDY if you 'Convert' the file to EPW.
The run period is a day -- which day you can control within the
SizingPeriod:DesignDay object. It gives EnergyPlus information for
the peak or design day for sizing HVAC equipment and systems. For
example, page 39 of the InputOutputReference has two examples--this is
the one for cooling design:
SizingPeriod:DesignDay,
Phoenix Sky Harbor Intl Ap Ann Clg .4% Condns WB=>MDB, !- Name
7, !- Month
21, !- Day of Month
SummerDesignDay,!- Day Type
35.8, !- Maximum Dry-Bulb Temperature {C}
12, !- Daily Dry-Bulb Temperature Range {C}
DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type
, !- Dry-Bulb Temperature Range Modifier Schedule Name
Wetbulb, !- Humidity Condition Type
24.5, !- Wetbulb at Maximum Dry-Bulb {C}
, !- Humidity Indicating Day Schedule Name
, !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
, !- Enthalpy at Maximum Dry-Bulb {J/kg}
, !- Daily Wet-Bulb Temperature Range {deltaC}
97342., !- Barometric Pressure {Pa}
4.1, ! Wind Speed {m/s}
260, !- Wind Direction {Degrees; N=0, S=180}
No, !- Rain {Yes/No}
No, !- Snow on ground {Yes/No}
No, !- Daylight Savings Time Indicator
ASHRAETau, !- Solar Model Indicator
, !- Beam Solar Day Schedule Name
, !- Diffuse Solar Day Schedule Name
0.588, !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub)
1.653; !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud)
Read the discussion of SizingPeriod:DesignDay in the
InputOutputReference beginning on page 33.
On Sat, Oct 27, 2012 at 2:41 PM, mohammad shar va balaaa
<mohammad_sharvabalaaa@xxxxxxxxx> wrote:
>
>
>
> what is a sizingperiod:designDay for this weather file?
> and what is the run period for that?
>
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/