Thankyou all for your replies - some very interesting pointers to papers and the indication of the sensitivity to solar.  I have gone back to the steady-state weather information and rechecked these and also found a rather annoying user (me) error in setting output variables.  Now the results are aligned to within 25% at it's worst and 3% at it's best.  Thankyou all again!

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, oscar hernandez <oscarhernandez_81@...> wrote:
>
> Hello,
> 
> It's normal. The objectif of a steady state simulation it's to see what happens on extreme conditions, fox ex, in winter, no occupation, no sun, lowest temperature, etc... you can know the power of your equipement (boiler, chiller, etc). You simulate the coldest day and the hotest day.
> 
> A dynamic simulation it's to know the behaviour of the building, when there are people, lights, equipements, etc.... the systems power and loads are lower than steady simulation, as you said 25-40% are normal values.
> 
> You can't compare theses simulations, steady simulation gives the real power systems and dynamic gives you the opportunity to optimise your building.
> 
> good luck!  
> 
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> From: direzionecontraria@...
> Date: Sat, 27 Oct 2012 14:53:40 +0000
> Subject: [EnergyPlus_Support] Re: dynamic vs. steady state (E+ significantly under predicting energy demands)
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
>  
> 
> 
> 
>   
> 
> 
>     
>       
>       
>       
> 
> 
> 
> I cannot answer, but utilization factor of heat gains has a great important in semi-steady state methods.
> 
> Try to read the following articles:
> 
> https://lirias.kuleuven.be/bitstream/123456789/204376/1/Whole+Building+IX+Comparison+of+steady-state+and+dynamic+building+energy+simulation+programs.pdf
> 
> http://www.sciencedirect.com/science/article/pii/S0378778806001861
> 
> With Regards a
> 
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Joe" <joebater@> wrote:
> 
> >
> 
> > does anyone have any idea why discrepancies between E+ and simple steady state calculations, e.g. Q = U.A.dT, are so severe?  despite it being a dynamic modelling approach you'd think that in the long term (e.g. a year) the two methods would have a reasonable harmony, instead I'm often finding 25-40% under-prediction in E+ compared to steady state for some simple buildings...
> 
> > is there a recommended report for building fabric heat losses?
> 
> > best regards and thanks in advance for any advice
> 
> > j.
> 
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/