Why do you want to control the chiller water temperture,
from the zone thermostat?
You can use a small chiller and/or large chiller to save
energy, when the demand changes.
When there is no cooling demand, the chiller is cycled on
and off by itself to maintain the water temperature you
have specified. (7°C to 12.5°C in plant sizing). You
can this temperature.
The master zone theremostat configuration controls the
complressor of the air to air AHU system with DX cooling
coil.
If you use the zone theremostat to turn off the chlller
and let the water temperature to rise to the ODT, there
may be a long delay to cool the water down again.
Dr. Li
To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
From:
wanghaojie630@xxxxxxxxx
Date: Wed, 31 Oct 2012 12:14:41 -0400
Subject: [EnergyPlus_Support] VAV AHU with Reheat
Control
Hi all,
I wonder if there is a way to control the chiller
based on the zone air
temperature when I use VAV AHU with reheat system.
People told me that
the the thermostat will only control the damper.
The chiller is
controlled by the setpoint manager for deck
temperature. If I only want
to control the chiller by zone air temperature,
how can I config this
system? Or I can only do this with CAV?
Thanks,
HJ