RE: [EnergyPlus_Support] Re: DOAS Outdoor Air Rate




Matthew,

Apart from using a ZoneControl:ContaminantController, I think what you want to do is either:

1.       Use Controller:OutdoorAir to force specific OA flow, something like:





Controller:OutdoorAir


Name


OAController_FitnessDOAS


Relief Air Outlet Node Name


NodeOut_EA_FitnessDOAS


Return Air Node Name


__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=27446/stime=1352238667>

Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmOWgwbjQ0BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzNTIyMzg2Njc->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkZzBiajgwBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzUyMjM4NjY3>Visit Your Group  | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use  | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe

__,_._,___