Glad to hear it! James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of ntraughpee Well the original work around was determining the max (assuming I used the same people schedule for each zone which is what I did since it was a decent enough representation) then determine what the FA requirement I would be looking for each zone then used the Controller:OutdoorAir to set my Minimum Outdoor Air Flow Rate to just under (95%) the peak value I'd be looking for then set the Maximum Outdoor Air Flow Rate to just over (105%)the peak value I was looking for. This worked like a charm but then after doing some more investigating I found the answer I was looking for in the Controller:MechanicalVentilation object. Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.