The reheat coil in the furnace does not operate using a set point manager. It operates to meet the zone sensible load as determined by the thermostat. If you want the reheat coil to be off, you will have to set the capacity to 0 or some small number. The heating coil in the furnace operates to meet the heating load and the reheat coil operates to meet the reheat load. This way you can separate the energy required for heating and reheating. On 11/18/2012 3:28 PM, Jean Marais
wrote:
Two options. 1) make the availibility of the gas furnace coil schedule always-0 or 2) set a setpointmanager:singelzone on the exit of the heating coil with the setpoint limits from say 4 low and 15 high...this will make the furnace coil only heat up air to a max of 15 degC and the reheat coil will do the rest of the work. -- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |