[EnergyPlus_Support] VRF DX cooiling coil, error due to Calculated outlet air RH greater than 1
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] VRF DX cooiling coil, error due to Calculated outlet air RH greater than 1
- From: "JFCS" <jamo0312see@xxxxxxxxx>
- Date: Tue, 20 Nov 2012 13:03:16 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 20 Nov 2012 06:03:19 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echo; t=1353416597; bh=NBKfHCWKUoB4nrmWhfFWTp6aqAl/xS49Jact5I9tWpk=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=i6Kl4j9yRD0EOBdXOz9vgC3aqCWCwY68tPbqm/ynKJ7445tAPHH+jYVALn7EqrrqnLyIltXU9/8qVhNKIb7DX8R4NSnbvPsjsUxADnwU3Pl92FUojkGCcd7d2ULiYZiA+mx9J0pkp+i0+5al1OSnLir7B09r/oBh5GDk9K1J5bU=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echo; d=yahoogroups.com; b=WKivKXUepfybyZcyyewtza/NTk0kKKwTo9pFiCrtFNrixlnbVeTdqkTJQUpsdCwlOUF7Kqed2ZbbBsPefs6RIwF7S1ez+sr0NJxTxL3OhMHXLo4VSSsD/GW0PTQeS35h92VcT++x+MGg+Hm8vmWej/7OhnQ74D7sImQSKwhZ3tQ=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
I am modeling a VRF system with given equipment parameters for "FCU 2B-7 VRF DX COOLING COIL"
how can i compute the "outlet air relative humidity"???
given for FCU 2B-7 VRF DX COOLING COIL:
Rated cooling Capacity=28kw
Rated sensible cooling Capacity=22.3kw
Rated air volume flow rate=1.183m3/s
Rated Condition= Indoor:27CDB/19CWB at Outdoor:35CDB
i'm generating errors as follows:
** Severe ** For object = COIL:Cooling:DX:VariableRefrigerantFlow, name = "FCU 2B-7 VRF DX COOLING COIL"
** ~~~ ** . The combination of
** ~~~ ** rated air volume flow rate, total cooling capacity and sensible heat ratio yields coil exiting
** ~~~ ** air conditions above the saturation curve. Possible fixes are to reduce the rated total cooling
** ~~~ ** capacity, increase the rated air volume flow rate, or reduce the rated sensible heat ratio for this coil.
** ~~~ ** If autosizing, it is recommended that all three of these values be autosized.
** ~~~ ** ...Inputs used for calculating cooling coil bypass factor.
** ~~~ ** ...Inlet Air Temperature = 26.67 C
** ~~~ ** ...Outlet Air Temperature = 13.17 C
** ~~~ ** ...Inlet Air Humidity Ratio = 1.125000E-002 kg/kg
** ~~~ ** ...Outlet Air Humidity Ratio = 9.866411E-003 kg/kg
** ~~~ ** ...Total Cooling Capacity used in calculation = 28000.00 W
** ~~~ ** ...Air Mass Flow Rate used in calculation = 1.615252 kg/s
** ~~~ ** ...Air Volume Flow Rate used in calculation = 1.400000 m3/s
** ~~~ ** During Warmup, Environment=SUMMER DESIGN DAY IN ORTIGAS AVE. GREENHILLS SAN JUAN CITY, at Simulation time=07/15 00:00 - 00:15
** Fatal ** Check and revise the input data for this coil before rerunning the simulation.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/