Dear Jean,

I am not quite certain that I understand your question ? but I?ll give an answer and you can tell me if I?ve helped?

·         As you know the amount of outdoor air is calculated by the E+ sizing objects and can also be manually entered.

·         As in real life, if you provide a specific amount of outdoor air to a single air system which serves several zones, the fraction of outdoor air which is part of the air loop (e.g., 10%) at the fan is the same fraction delivered to every zone.  In this example, 10% of the airflow to every zone is outdoor air.

·         If you truly need to have very different outdoor air fractions in each zone, you must define a separate air loop for these zones with the correct amount of outdoor air in each zone.

·         Alternatively, a DOAS is commonly used to provide the minimum outdoor air flow to each zone (plus a zone heating / cooling component such as radiator, fan coil, etc.)




__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=27593/stime=1353681431>

Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmY3A2cnBjBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzNTM2ODE0MzE->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkYzF2Z2I1BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzUzNjgxNDMx>Visit Your Group  | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use  | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe

__,_._,___