|
Dr.Li,
Thank you first! I have ran the example model named
"IceStorage-Series-ChillerUpstream", it has the same problems as I did. Once you
turn the output interval from hourly to timestep, the same fluctuations showed
up for parameters such as
Detailed Ice Thermal Storage Mass Flow Rate and
chilled water loop temperatures during ice charging period, in my opinion, it is
due to the internal control algorithms and it will start and shut down the
system too frequently around the turnoff temperature which is set in the low
temp turn off availability manager. In addition, the chilled water flow rate
schedule is set to always unit one, which would also confuse me. If you set the
pump operation mode to Intermittent, no ice will be made in the night charging
period. You can have a try on the example files. Thank you again and I am
looking forward to your reply!
Zuo Mingming
From: YuanLu Li
Date: 2012-11-30 21:10
Subject: RE: [EnergyPlus_Support] Unstable control during
thermal charging period with Ice storage tank.
Have you ran the example file on Ice storage?
This example reduce the chiller temperture to -5°C when the chiller load is light or not required, so that ice can form on it.. In order to make ice the temperature of the coil in the storage tank has to be low. There are a number of steps mentioned in the example that described special requirement. There is dummy load during the ice making time, etc. The ice is formed on the chiller coil in the storage tank, and the pump is in the water loop. What you are describing seems to be tying to make ice while the water loop is still active to provide buiding cooling. I have not look at your IDF yet. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: icesand@xxxxxxx Date: Fri, 30 Nov 2012 08:20:39 +0000 Subject: [EnergyPlus_Support] Unstable control during thermal charging period with Ice storage tank. Hi all,
I have composed a model with ice storage tank, but supecious fluctuations of chilled water flow as well as charging performance are detected. The problems are as below: 1. the primary chilled water pump has to be set to continous mode, otherwise the ice tank will never have any charging energy. 2. once this pump is under continous mode, fluctuations of the node parameters come about. For example, chiller evaporator inlet temperature changes from 7C to -5C every timestep. The low temperature tunoff manager has been used in this model. Would you please help me find the possible solutions? Thank you all in advance and the idf file named "Thermal energy storage Test" has been uploaded to the files of this group. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |