[EnergyPlus_Support] Re: Variable Refrigerant system
Thank you very much RRaustad!
The missing parameter was
- Variable Refrigerant Flow Heat Pump CrankCase Heater Electric Consumption
I added this parameter and the sums match. Regarding the fan energy I didn't include it because is counted separately in the html results (cooling, heating and fans are shown separately).
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, RRaustad@... wrote:
>
> You forgot to include the fan energy. Crankcase heater energy is also a
> missing component as is evaporatively cooled condenser pump power if
> you are using these options.
>
> Zone Terminal Unit Cooling Electric Consumption
> Zone Terminal Unit Heating Electric Consumption (for all zones)
>
> These are the parasitics related to the terminal unit's parasitic
> inputs and depends on which mode (cooling or heating) the system is
> currently operating in.
>
> ZoneHVAC:TerminalUnit:VariableRefrigerantFlow,
> 30, !- Zone Terminal Unit On Parasitic Electric Energy Use {W}
> 20; !- Zone Terminal Unit Off Parasitic Electric Energy Use {W}
>
>
> Variable Refrigerant Flow Heat Pump Cooling Electric Consumption
> Variable Refrigerant Flow Heat Pump Heating Electric Consumption
>
> These should provide the outdoor unit electric consumption. Adding
> these should give the total outdoor unit electric consumption over the
> year.
>
> Variable Refrigerant Flow Heat Pump Electric Defrost Consumption (
>
> The is the electric consumption due to defrost. After reviewing the
> code, I am not exactly sure if this is included in Variable Refrigerant
> Flow Heat Pump Heating Electric Consumption since the calculation of
> defrost energy is indirectly included in total electric consumption as
> a fraction of energy use. I do see that defrost electric consumption is
> included in the operating COP calculation which infers it is a seperate
> energy use calculation.
>
> Carefully review the sum of all inputs to the model (fan + terminal
> unit parasitics + outdoor unit electric consumption + defrost + evap
> condenser pump + basin heater electric consumption)
>
>
>
>
> On Fri, 07 Dec 2012 19:34:47 +0000 rikards2342 <migue885@...>
> wrote:
> > Dear community, I simulated a variable refrigerant system with 8
> > AirConditioner:VaribleRefrigerantFlow (8 external units) and a lot of internal
> > units. The simulation results are correct, but I want to know the individual
> > electric consumption of each external unit and in the html table only appears
> > the total consumption of all HVACs (section end uses, heating and cooling).
> > I tried to sum (using output:variable results in excel) the following items:
> >
> > - Zone Terminal Unit Cooling Electric Consumption
> > - Zone Terminal Unit Heating Electric Consumption (for all zones)
> > - Variable Refrigerant Flow Heat Pump Cooling Electric Consumption
> > - Variable Refrigerant Flow Heat Pump Heating Electric Consumption
> > - Variable Refrigerant Flow Heat Pump Electric Defrost Consumption (for all
> > external units)
> >
> > But the sum of these parameters isn't the same that the sum of the heating and
> > cooling electricity given in the html results table. The difference is very
> > small.
> >
> > Anyone knows which is the parameter I don't take into account?
> >
> > Thank you very much in advance!
> >
> > ------------------------------------
> >
> > Primary EnergyPlus support is found at:
> > http://energyplus.helpserve.com or send a message to
> > energyplus-support@...
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are currently allowed but be mindful that not everyone has a high
> > speed connection. Limit attachments to small files.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/