Helia,
I think your cooling load issue was likely to have been caused by your having partition constructions set as externally adjacent surfaces, See my first post for an IDF that should correct this issue. In general partitions should never have sun/wind/outdoor adjacency.  

Below are copy/paste's of what I believe your problem to be, Best of regards-

Name Partitions: Adiabatic
Outside Layer 1/2IN Gypsum
Layer 2 9_RVAL_2
Layer 3 1/2IN Gypsum


Name Obj:0001 Obj:0002 Obj:0003 Obj:0004
Surface Type WALL WALL WALL CEILING
Construction Name Partitions: Adiabatic Partitions: Adiabatic Partitions: Adiabatic Partitions: Adiabatic
Zone Name Main_Room Main_Room Main_Room Main_Room
Outside Boundary Condition Outdoors Outdoors Outdoors Outdoors
Outside Boundary Condition Object
Sun Exposure SunExposed SunExposed SunExposed SunExposed
Wind Exposure WindExposed WindExposed WindExposed WindExposed
View Factor to Ground 0.50000 0.50000 0.50000 0.00000
Number of Vertices 4 4 4 4
Vertex 1 X-coordinate 7.20000 7.20000 3.20000 3.20000
Vertex 1 Y-coordinate 8.30000 5.30000 8.30000 8.30000
Vertex 1 Z-coordinate 3.00000 3.00000 3.00000 3.00000
Vertex 2 X-coordinate 7.20000 7.20000 3.20000 3.20000
Vertex 2 Y-coordinate 8.30000 5.30000 8.30000 5.30000
Vertex 2 Z-coordinate 0.00000 0.00000 0.00000 3.00000
Vertex 3 X-coordinate 3.20000 7.20000 3.20000 7.20000
Vertex 3 Y-coordinate 8.30000 8.30000 5.30000 5.30000
Vertex 3 Z-coordinate 0.00000 0.00000 0.00000 3.00000
Vertex 4 X-coordinate 3.20000 7.20000 3.20000 7.20000
Vertex 4 Y-coordinate 8.30000 8.30000 5.30000 8.30000
Vertex 4 Z-coordinate 3.00000 3.00000 3.00000 3.00000



Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
  





On Sun, Dec 23, 2012 at 12:29 PM, Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx> wrote:
Helia, 
If you model a basecase without PCM you should use the same CFD algorithm and settings for the no pcm case, this is why I changed the Heat Balance settings.
 Without a weather file is can not be said if your cooling loads are from solar or another factor, but knowing that you are in Iran, I assume that your weather file would be a dry hot climate, but am unsure the actual location. Possibly you could attach or reference your weather file.  For adiabatic walls you will not want to have sun or wind or outdoors in your adjacency choices, In the previous file I changed them to zone so that the other side of the internal wall partition is assumed to be the same as the zone temperature, but surface or adiabatic would also work for modeling a partition. 


Linda,
I did update using the version updater.  Not sure why, but after running version updater and running the file did not have a building object.  I just re-ran the file through version updater and ep launch and have attached the files showing this issue. (possibly a bug when going from V5 to V7.2??)  




Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
  





On Sun, Dec 23, 2012 at 10:26 AM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
 

The original file DOES have a building object.  The title says "Without PCM".  Why didn't you just convert the file using the version updater, Jeremiah?

Also, we have no indication what weather file is being used?



At 10:46 AM 12/23/2012, Jeremiah Crossett wrote:


Helia,
Sounds like solar loads to me. Hey so I noticed that four of your surfaces where titled to be adiabatic but where actually set to be externally adjacent, that your file was in E+  5, that you had no building object and that you where running at 12 timesteps. Also I noticed you mention PCM in the file name. I went ahead and updated your file and fixed some issues and have attached it to this email. Possibly your summer cooling loads will make more since with this updated version.


Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
www.phasechange.com
  []





On Sun, Dec 23, 2012 at 6:23 AM, Helia Taheri < helia_taheri2003@xxxxxxxxx> wrote:
 

Hi

I have problem in cooling load!!!!
The results are very non logical. For example in all of the days of July, we have a lot increase in cooling load between 8am to 8pm. Although I don't have any people and light schedule.
Thanks alot.

Best Regards,
Helia Taheri





Content-Type: application/octet-stream;
         name="13910930 Win 2x1 EP7 Without PCM DIVA new.idf"
Content-Disposition: attachment;
         filename="13910930 Win 2x1 EP7 Without PCM DIVA new.idf"
X-Attachment-Id: f_hb2gwsut1





__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.