|
It depends what you want to use if for. If it is for an HVAC outdoor air inlet node (like a rooftop package) then you can apply it directly to the “Outdoor Air System Node” actuator. If you want to actuate the weather data for the entire model, then you’d need a separate, clean signal for the sensor since the actuator will step on it. For a clean signal, I would make a Schedule:File generated from a previous run by reporting the value. Then the EMS sensor goes on “Schedule Value.” For this kind of prescribed change to weather, another way to go with no EMS is to modify the weather file. Using WeatherConverter, you would go from EPW to CSV, modify in CSV, then convert back to EPW. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of hnoboam OK, thanks. Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |