I hope you've also noticed that there's a time lag of about 90 days, i.e., minimum soil temperature occurs about 3 months after minimum air temperature. The appropriate depth depends on what type of foundation the building has. Most large commercial buildings all have an underground space or basement, for which you should use the soil temperature at 2 m. Another problem is that buildings have a big effect on the soil temperature, heating it in the winter and cooling it during the summer. There's a Slab program that allows you to calculate better soil temperatures accounting for the effects of the building itself. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 1/18/2013 5:49 PM, academicryan wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.