Re: [EnergyPlus_Support] azimuth mismatch for horizontal surfaces





First off, walls are not usually flat.

That may be a clue.

If it is a floor/ceiling, EnergyPlus applies different rules.

At 02:44 PM 1/22/2013, Cody Rose wrote:
Hello,

I received the following warning:

    ** Warning ** GetSurfaceData: InterZone Surface Azimuths do not
match as expected.
    **   ~~~   **   Azimuth=270.0, Tilt=180.0, in
Surface=0J8KFINJV0B9CVEUNR2CDF, Zone=PLENUM
    **   ~~~   **   Azimuth=180.0, Tilt=0.0, in
Surface=14KF$QRCJ1HQWVE7M35$CE, Zone=BANKING FLOOR
    **   ~~~   ** ..surface class of base surface=Wall

The surfaces in question are defined as follows:

   BuildingSurface:Detailed,
     0j8kFINjv0b9cVEuNR2cdf,  !- Name
     Wall,                    !- Surface Type
     04 | CStone 04 (0.050),  !- Construction Name
     Plenum,                  !- Zone Name
     Surface,                 !- Outside Boundary Condition
     14kF$qRcj1hQwve7M35$Ce,  !- Outside Boundary Condition Object
     NoSun,                   !- Sun Exposure
     NoWind,                  !- Wind Exposure
     Autocalculate,           !- View Factor to Ground
     Autocalculate,           !- Number of Vertices
     20.149,20.898,4.05,  !- X,Y,Z ==> Vertex 1 {m}
     23.894,19.962,4.05,  !- X,Y,Z ==> Vertex 2 {m}
     23.894,8.085,4.05,  !- X,Y,Z ==> Vertex 3 {m}
     20.149,8.085,4.05;  !- X,Y,Z ==> Vertex 4 {m}

   BuildingSurface:Detailed,
     14kF$qRcj1hQwve7M35$Ce,  !- Name
     Ceiling,                 !- Surface Type
     04 | CStone 04 (0.050),  !- Construction Name
     Banking Floor,           !- Zone Name
     Surface,                 !- Outside Boundary Condition
     0j8kFINjv0b9cVEuNR2cdf,  !- Outside Boundary Condition Object
     NoSun,                   !- Sun Exposure
     NoWind,                  !- Wind Exposure
     Autocalculate,           !- View Factor to Ground
     Autocalculate,           !- Number of Vertices
     20.149,20.898,4,  !- X,Y,Z ==> Vertex 1 {m}
     20.149,8.085,4,  !- X,Y,Z ==> Vertex 2 {m}
     23.894,8.085,4,  !- X,Y,Z ==> Vertex 3 {m}
     23.894,19.962,4;  !- X,Y,Z ==> Vertex 4 {m}

I'm not sure how EnergyPlus handles the "azimuth" for horizontal
surfaces like these, so I don't know if I need to worry about this
warning. In either case I'd like to know how to fix it, though.

Thank you,
Cody Rose


------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___