|
Another issue to consider is the tolerance for what constitutes not meeting setpoint. One can use the OutputControl:ReportingTolerances object to control how far from setpoint counts as being unmet. If you don’t use that object then the default is only 0.2C. 90.1 isn’t too clear on this point, but it seems one can use a value appropriate for the real building’s thermostat throttling range which likely higher than 0.2C. I believe a tolerance value of 0.55C matches DOE-2’s definition of an unmet hour and so is probably consistent with the original intent behind the 300 hour criterion. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of luke_dorna If your thermostats are set up the way you like, and you are still not meeting your load hours even with autosized equipment there are other steps you can take. If unmet load hour appear to be happening equally across your model use the Sizing:parameters object to oversize your entire hvac system to meet the peak loads. Sizing:Parameters, 1.25, !- Heating Sizing Factor 1.15, !- Cooling Sizing Factor 4; !- Timesteps in Averaging Window If the problem appears to be isolated to a single thermal zone you can use the section highlighted below in the sizing:zone object to increase the capacity for just the zone in question. Sizing:Zone, f1:airlineops216, !- Zone or ZoneList Name SupplyAirTemperature, !- Zone Cooling Design Supply Air Temperature Input Method 12.8, !- Zone Cooling Design Supply Air Temperature {C} , !- Zone Cooling Design Supply Air Temperature Difference {deltaC} SupplyAirTemperature, !- Zone Heating Design Supply Air Temperature Input Method 32.0, !- Zone Heating Design Supply Air Temperature {C} , !- Zone Heating Design Supply Air Temperature Difference {deltaC} 0.0085, !- Zone Cooling Design Supply Air Humidity Ratio {kgWater/kgDryAir} 0.0080, !- Zone Heating Design Supply Air Humidity Ratio {kgWater/kgDryAir} SZ DSOA F1:AIRLINEOPS216,!- Design Specification Outdoor Air Object Name , !- Zone Heating Sizing Factor , !- Zone Cooling Sizing Factor DesignDay, !- Cooling Design Air Flow Method , !- Cooling Design Air Flow Rate {m3/s} , !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2} , !- Cooling Minimum Air Flow {m3/s} , !- Cooling Minimum Air Flow Fraction DesignDay; !- Heating Design Air Flow Method --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Nino Letti wrote: __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |