It's quite common that attic temperatures can fall below the outdoor air temperature on clear cold nights due to night sky radiation from the roof. I've seen measured data for residential attics where the temperature depression is around 3-5 F in California and 1-2 F in Florida. 5C or 9F seems pretty large, but not outside the realm of possibility. I don't know what night sky radiation model is currently in EnergyPlus, but in DOE-2 it was based on work done by Marlo Martin at LBNL back in the early 1980's and produced similarly large attic temperature depressions (10F below ambient in some runs I did for California houses) that I have found doubtful. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx www.whiteboxtechnologies.com (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 2/5/2013 3:26 PM, Griffith, Brent wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.